Compressor and Blower Fan both don't start up on HVAC
lbeachmike
lbeachmike Member Posts: 215
I have a Lennox Model XC16-024-230-02 condenser and CBX27UH-036-230-6-02 blower unit. When the thermostat is calling for cooling, the fan on the condenser turns on but the compressor does not. I can hear the compressor humming but not starting up. At the same time, the blower motor does not start up (but also seems to hum). If I turn the thermostat to Fan On, the blower fan also does not start up.
I thought this might be one leg of power failed, but the condenser and blower units are on two totally different double-breakers.
Any ideas?
    mattmia2 Member Posts: 15,985
    edited August 2025
    did you check voltage between lines and between each line and neutral?
    Are you sure the compressor hasn't been not working for a while and you didn't just notice it until the indoor blower stopped?
    is this a single phase 120/240 v service?
  • lbeachmike
    I am certain the compressor has been working. We have two units in our house - this unit is for the upstairs. We only use it at night when we go up to sleep in the upstairs bedroom. If the compressor was not working, it would have been super-hot and super-stuffy. The cooling has been normal. As you know, the compressor also has a very distinct sound when on. It would have been very noticeable in both regards.
    I have not checked any voltages anywhere yet. I was going to check voltage coming into the contactor to make sure I see 240V there. But it also feels rather pointless, given that the blower does not turn on even by turning on only the fan.
    As far as I am aware, I have single phase 120/240 service.
    pecmsg Member Posts: 6,878
    If your concerned dealing with high voltages call a contractor
  • neilc
    neilc Member Posts: 3,139
    could be caps, could be motors, could be contactors,
    your meter knows,
    known to beat dead horses
    HVACNUT Member Posts: 7,305
    It seems odd that both the compressor and indoor blower motor failed at the same time. Definitely check the voltage, but the downstairs system is fine, so maybe caps on both? Any surges in your area?
    EdTheHeaterMan Member Posts: 11,748
    I'm betting on the Capacitors. here is a way to check them without a Capacitor tester, all you need is a volt meter with an amp probe.
    EBEBRATT-Ed Member Posts: 19,881
    Harbor Freight has chepo meters that include capacitor testing for about $20.
    My cousin goes to FLA in the winter and forgot to bring the meter I gave him. Got one at HF for about $20
    the meters i have had with capacitance meters built in have only read to like 1000 pf.
    109A_5 Member Posts: 3,684
    Weird or odd behavior, always check the power first under load.