Heat Pump Cooling Not Working
Just found that somehow, the compressor now can start. I can see the amp draw when start and current is stable at ~5A while running.
However the pipe is not cold yet will verify a bit further after work.
You're pretty much right there. The reading across Run and Start should be roughly the sum of the other 2 readings. Should be 3.5. Actual is 3.7. I like it. 👍
Try a Hard Start Capacitor/Relay.
Now that my compressor is running.
I compare the running currency of the working unit vs not cooling unit. 6.6A vs 5.9A. Slightly lower indicating the compressor is not working as hard as it should be?
Opening up the outdoor unit a bit more. Suction side is only slightly cold (not cold enough comparing with working unit). I use my hand to feel the temperature of other lines in the outdoor unit and mark in the picture. The air blown out by the fan is not that warm (comparing with working unit).
Does this mean the system is working, but not as well as it should be? Indicating low on refrigerant?
With the outdoor unit running, what's going on with the indoor unit (the evaporator and the blower). The "Very Hot" on the compressor output means the compressor is doing something. At this point the refrigerant charge should be verified.
One Pipe System0 -
@heatingrabbit , time to call a pro.
Consulting1 -
I check the manual the unit is using R22 refrigerant, only licensed person can handle it. Plan to call HVAC specialist.
I would agree R-22.
One Pipe System0 -
HVAC company come and check the charge. There is no r22 left in the system.
However they don't recharge r22 anymore and can only install a new system with new refrigerant.
Seems not something fixable as r22 was phased out?
Start components (cap and relay) are optional
Most all units have no pressure switches
If you get ohm readings between common-start and common-run on compressor these two readings should add up to the start-run reading (approximately)
Then if the compressor motor is not hot to touch and you have no readings from common or start or run to ground the compressor should start
Done is done. The question now is, will the new system be 454B or R32?
Some folks are still doing R-22 work.
R22 Trane AC leaking patch spine fin coil
One Pipe System0 -
There are R-R-22 replacements but if the system is old its time to go.