Lochinvar knight lockout
The system keeps locking out after i reset it
The indirect tank is reading 89° on the gauge
Should i ohm out the sensors and see if they’re bad?
where is sensor number one and number 2? sounds like it isn't circulating
first photo is the system sensor,
Second is the Indirect tank sensor
i agree, circulator is most likely dead. water is not moving thru the boiler casing a high delta thru the boiler.
so I’ve reset it again, it ran for 4min before locking out again. The outlet side going to the tank was getting hot and the return going through the circulator and to the inlet were warming up. I don’t have the magnetic tester to see if the pump is actually spinning but it is letting hot water through and i do feel it vibrating.
The circulator is a grundfosTYPE:ups15-58cifc
didn’t quote your reply but i posted the pics of the sensor locations
are you sure those are the sensors? there are probably half a dozen temp sensors at various points. what makes you think those are number 1 and 2? one looks like the system or dhw recirc sensor and the other looks like the dhw tank sensor.
One Pipe System0 -
I would agree the circ is not moving water. Could be an air lock somewhere or a failed circ
What is the boiler pressure? Boosting fill pressure some times help clear an air bubble.
Don’t bet the farm on those spinner tools.
It really just indicates there is power at the motor. A demo here.
If the system is allowed to sit idle for a while, do the temperatures the system displays for Sensor 1 and Sensor 2 seem plausible (basically approaching ambient temps) ? If so I still think it's a water flow issue through the heat exchanger.
One Pipe System1 -
You need to post a pic of the piping of your boiler. There is more than 1 way to pipe the indirect and you have to make sure that it is identified in the boiler if you accidentally changed the parameters around
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 111 Geothermal
- 163 Indoor-Air Quality
- 72 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 55 Water Quality
- 48 Industry Classes
