Lochinvar knight lockout

Mjoe989
Mjoe989 Member Posts: 4
image.jpg

The system keeps locking out after i reset it

The indirect tank is reading 89° on the gauge

Should i ohm out the sensors and see if they’re bad?

Comments

  • mattmia2
    mattmia2 Member Posts: 13,756

    where is sensor number one and number 2? sounds like it isn't circulating

  • Mjoe989
    Mjoe989 Member Posts: 4
    image.jpg image.jpg

    first photo is the system sensor,

    Second is the Indirect tank sensor

  • pedmec
    pedmec Member Posts: 1,233

    i agree, circulator is most likely dead. water is not moving thru the boiler casing a high delta thru the boiler.

  • Mjoe989
    Mjoe989 Member Posts: 4

    so I’ve reset it again, it ran for 4min before locking out again. The outlet side going to the tank was getting hot and the return going through the circulator and to the inlet were warming up. I don’t have the magnetic tester to see if the pump is actually spinning but it is letting hot water through and i do feel it vibrating.

    The circulator is a grundfos

    TYPE:ups15-58cifc

  • Mjoe989
    Mjoe989 Member Posts: 4

    didn’t quote your reply but i posted the pics of the sensor locations

  • mattmia2
    mattmia2 Member Posts: 13,756

    are you sure those are the sensors? there are probably half a dozen temp sensors at various points. what makes you think those are number 1 and 2? one looks like the system or dhw recirc sensor and the other looks like the dhw tank sensor.

  • 109A_5
    109A_5 Member Posts: 2,553
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • hot_rod
    hot_rod Member Posts: 25,443

    I would agree the circ is not moving water. Could be an air lock somewhere or a failed circ

    What is the boiler pressure? Boosting fill pressure some times help clear an air bubble.

    Don’t bet the farm on those spinner tools.

    It really just indicates there is power at the motor. A demo here.

    IMG_0797.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • HVACNUT
    HVACNUT Member Posts: 6,929

    As mentioned, its not the tank sensor. The boiler has inlet an outlet temperature sensors.

    Screenshot_20250814_064023_Samsung Notes.jpg Screenshot_20250814_064055_Samsung Notes.jpg
    Mjoe989mattmia2
  • 109A_5
    109A_5 Member Posts: 2,553

    If the system is allowed to sit idle for a while, do the temperatures the system displays for Sensor 1 and Sensor 2 seem plausible (basically approaching ambient temps) ? If so I still think it's a water flow issue through the heat exchanger.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System