How many btu/hr from this cast iron radiator?

Options
kinghoward
kinghoward Member Posts: 23

Studied all the charts and tables but still need help. This is an old cast iron radiator about 3 ft high. It has three columns and is about 9 inches wide. On one end, about 2 ft up, is a bleeder screw. There are 12 'sections?' along the length of about 30 inchs. Assuming 160 F degree water, what is a good estimate of btu/hr that can be emitted if this radiator is half full of water? I beleive its an old steam radiator…when I try to bleed out air, it fills to the level of the screw and water comes out, so cant fill it any higher by myself? The bottom of this radiator gets quite warm but never so hot that I cant hold my hand on it. Its at the end of the return line. I hope this is enough info. If you want a pic, I can do that. Its a big heavy old one, kinda cool.

Comments

  • mattmia2
    mattmia2 Member Posts: 17,208

    there should be a low tapping for a steam vent and a high tapping for a hot water bleeder.

    why do you need to know the output?

  • Steamhead
    Steamhead Member Posts: 18,625

    Definitely sounds like a steamer. Post a pic from the front and the side where the bleeder is, and we'll have a look.

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

  • kinghoward
    kinghoward Member Posts: 23

    Nope, sorry, somebody put only one bleeder screw on the side. No more at the top. I dont have that many hydronic baseboards on this loop, I am just wondering if this radiator emits more btu per foot of length just in case I replace it with baseboards. Thank u

  • mattmia2
    mattmia2 Member Posts: 17,208

    the output of a radiator is far more than a couple feet of cast iron baseboard. if the radiator is connected at the top so that it is compatible with hot water, it should have a tapping near the top and a tapping about 2/3 of the way down. you plug the top tapping and use the lower tapping for steam, you plug the lower tapping and use the upper tapping for hot water.

  • kinghoward
    kinghoward Member Posts: 23
  • 109A_5
    109A_5 Member Posts: 4,158

    Steam only radiators work poorly with hot water since the top of the sections are not connected together so air is trapped. The sections of the radiator pictured are connected at the top (Red Arrow) so it will work with either Steam or Hot water.

    One example, typical places for venting / air bleeding.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    kinghoward
  • mattmia2
    mattmia2 Member Posts: 17,208

    being piped in copper that is not the original home of that radiator. that tapping is for the steam air vent. look for a probably slotted plug near the top.

    that is a common earlier radiator, others will know it. possibly an arco rococo. (arco is american radiator company, now american standard)

  • 109A_5
    109A_5 Member Posts: 4,158
    edited August 2025

    That looks like a steam only radiator, the sections are not connected at the top. Even though you can bleed that end section to the bleed port level the rest of the radiator is probably mostly air bound.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • kinghoward
    kinghoward Member Posts: 23

    The house was built around 1918. I doubt that radiator has ever left that room, I concur somebody attached some 3/4 copper piping later but it fits perfect in one spot. It does put out some heat, doesn't seem to be a way to fill it with water but will look again. No idea how old the radiator is, but thanks again!

  • mattmia2
    mattmia2 Member Posts: 17,208

    it was all the same picture when i looked at it earlier so i couldn't see the top. yeah, that radiator isn't compatible with hot water unless you drill and tap a bleeder in the top of each section. it is steam only.

  • 109A_5
    109A_5 Member Posts: 4,158

    At this point the BTU/Hr may be irrelevant since there is only water flowing through maybe only 10 % of the radiator.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • kinghoward
    kinghoward Member Posts: 23

    I learned alot. Thanks everyone.

  • Steamhead
    Steamhead Member Posts: 18,625

    Looks like an American Rococo, and yes, it is steam-only. It cannot have been original to that system.

    Please do not desecrate it by drilling and tapping for bleeders on each section. You can probably arrange some sort of trade with someone who has a hot-water Rococo. That one you have is 60 square feet.

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

    109A_5
  • mattmia2
    mattmia2 Member Posts: 17,208

    it is more that most of it isn't filled. cast iron radiators that are filled with water but only have the bottom tapings used for the supply and return work fine because they heat by convection of the water in the columns.

    does the room heat adequately? what sort of baseboard does it share a circuit with, is it cast iron baseboard or fin tube?

    looks like someone that didn't know what they were doing tried to convert it from steam to hot water if the return is copper and the supply is black iron.

  • 109A_5
    109A_5 Member Posts: 4,158

    To me 10 % full or 90 % empty accomplishes the same thing, nowhere near the rated heat transfer to the surrounding environment as compared to when it is used correctly, steam. With a correct Cast Iron radiator for hot water, even if the supply and return is at the bottom I find it hard to believe the water at the top is 100% stagnant.

    The thing is, if you need much more heat in that room when it is cold out, the best practice is to put the correct radiator in that place.

    How that steam radiator got there we may never know. It simply may have been a mistake and it never worked well. It would not be the first time an installer screwed something up. Maybe the home had a steam to hot water conversion that was not done as correctly as it should have. Maybe the owners back then did not care, or did not realize the issue, so it was never corrected.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • kinghoward
    kinghoward Member Posts: 23

    I think it is a situation where the steam radiator was there, so somebody erroneously thought they could just hook up some water and stick a bleeder valve on it. I have 'fin' baseboards (copper pipe) on a short loop and just ended the loop with this cast iron because it was there, might as well try to use it. I agree do not desecrate this wonderful radiator. Finding someone to take it from upstairs isnt going to happen here, ha! But it should be preserved.

  • Steamhead
    Steamhead Member Posts: 18,625

    Where's "here"? We might know someone……………

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

  • kinghoward
    kinghoward Member Posts: 23

    Hi steamhead to respond to your question we are in NW Minnesota. We decided to leave the cast iron radiator as is for now and will revisit the topic next year. Cheers, kinghoward