boiler replacment opinion on the West Coast

Alister
Alister Member Posts: 2

I’m a home owner and am looking for some opinions to cross reference the bids of installers. Many seem to steer me to a boiler and tankless water heater. My triangle tube solo boiler for heat and my Takagi 3 tankless water heater for DHW needs to be replaced soon so I’d appreciate some feedback. I live on the coast of San Francisco. My house has staple up floor hydronic heating zones and the walls are insulated with R13 and floors and ceiling at R30. I’ve done a rough total house heat loss calculation of 35K. We have 2 full time residents but run a regularly booked Airbnb frequently with 4 guests

In looking back and with current research it seems my installer did not account for the value of stored thermal mass even though I have a decent size mechanical room.

Now that gas and electricity costs are much higher, I’m thinking of going with a Viessman Vitodens 200 boiler, 80 or 120 gal Vitocell 300 indirect tank for DHW. I’m also considering 2-3 solar thermal panels now or in the future. I'm mainly interested in the Viessman for the integration and ease of installation even though it's more expensive.Any thoughts or advice would be appreciated.

Mad Dog_2

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 26,299
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Alan (California Radiant) Forbesrick in Alaska
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,426

    Viessman is considered top of the line if you have someone who knows how to service them. To me tankless water heaters are problematic.

    EdTheHeaterManmattmia2Mad Dog_2
  • hot_rod
    hot_rod Member Posts: 25,543

    Air to water heat pumps are common in that area, climate is a good match, incentives are available.

    Corey Page posts a lot of HP conversation on his IG account, in that area

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,914

    In your situation, I like the indirect water heater idea.  Viessmann is a good product. Is there a Energy Kinetics dealer nearby?  They basically invented the Thermal Purge control system, for their residential boiler systems, years ago.  That will offer additional savings. 

    Just a thought

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Roger
    Roger Member Posts: 421

    Thank you for thinking of us, @EdTheHeaterMan , although we do not have distribution in Northern California.

    Best,

    Roger

    President
    Energy Kinetics, Inc.
  • mattmia2
    mattmia2 Member Posts: 13,943

    There are a number of other manufacturers that have similar integrated controls to the viessman now too.

  • Alan (California Radiant) Forbes
    Alan (California Radiant) Forbes Member Posts: 4,535
    edited August 6

    I have the same setup as you are suggesting except my Viessmann (V.) is a 100 series. No need for the 200 unless you have lots of peripheral equipment (mixing valves, solar, etc.).

    I service many V. boilers in the City, East Bay, Marin and South Bay and stock the most common replacement parts as, unfortunately, parts are not available locally. I urge my customers to stock these parts there, with the boiler in case I run out or if they call in someone else for repairs.

    The 120 gallon indirect sounds too big for you. I’d go with the 80 gallon. V. has the best stainless indirects. None of the ones I’ve installed over the last 40 years have failed.

    Lochinvar also makes a great boiler and they, along with V. have good technical support.

    Edit:

    "In looking back and with current research it seems my installer did not account for the value of stored thermal mass even though I have a decent size mechanical room."

    Stored thermal mass? I don't understand.

    "I’m also considering 2-3 solar thermal panels now or in the future."

    Oh, I see. The solar add on is why you wanted the 200 Vitodens. I'd skip the solar thermal. Too expensive to maintain and repair. Solar electric is a better option.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab