Utica Combi Boiler (MAC-150)-Error 133- Causing big bang noise after few trial of combustion
Hello All,
I have Utica combi Boiler ( Model # MAC-150) installed few years ago. Lately it is throwing 133 error . I just cleaned the Flame sensor but still it is throwing 133 error after few times trying to get ignite when hot water calls.
Heating is off by the way.
Also when it ignites after few trials it makes a loud ignition bang noise that is scary .
Please advise what needs to be done to resolve 133.
Condensate line checked— Not clogged
Gas line—-3/4" sized…
Thank you,
Hiren Patel
Was everything on the list for that error verified ? If the spark is poor OR not where it needs to be it won't work correctly.
Yes you are absolutely right.
Thank you,
Hiren Patel0 -
I had the same issue. It ended up with the igniter being deformed or bent so much. I bought a new one and run auto calibration procedure per instructions coming with the part. I believe this is a design flaw. Anybody having the same issue should check the igniter.
- 15.8K Strictly Steam