AWHP - Plate heat exchanger or not?

Hello,
I'm looking at options for air to water heat pump systems. This would be for space heat and DHW using a reverse indirect buffer tank.
Some manufacturers system designs call for the AWHP to directly heat the buffer tank, with the entire tank and hydronic zone loops being glycol mix. Other manufacturers (US Boiler) suggest a plate exchanger between the AWHP and the buffer tank, with glycol only in the outdoor heat pump loop.
If I understand, the pros for the exchanger are:
- Less glycol. A buffer tank worth of glycol mix isn't cheap, and if you need to drain the system, you would need to deal with all of that mix.
- Better heat transfer / easier pumping in the hydronic zones and indirect tank without glycol.
Cons:
- More parts: heat exchanger, additional circulator, valves, etc. Probably eat up the cost of glycol savings.
- Loss of efficiency through the exchanger, critical to get flow rates / Delta T correct.
Thoughts?
Thank you.
Comments
-
I am having this same debate with myself. I have an AWHP system that currently services a portion of my house, with the eventual goal to expand the system to cover my whole house. I currently have the entire system filled with glycol. While this has worked OK for the last couple years, I am considering installing a heat exchanger and switching the indoor portion to water for the following reasons:
- I have had one leaky fitting on a fan coil in a bedroom. Thankfully it was minor, I caught it quickly, and the bedroom floor is vinyl so nothing was damaged. But its a lot easier to clean up water than glycol if a leak occurs. A catastrophic failure would result in not only a mess to clean but also require purchasing more expensive glycol
- I don't want to deal with draining and storing up to 100 gallons of glycol if/when I need to add or replace a component
- One of my fan coil emitters is pretty undersized, the reduced heat transfer of glycol is not helping this situation, especially in cooling season when the glycol becomes more difficult to pump due to low temp and I'm losing both flow rate and heat transfer
I'm not a professional, just a guy who has been living with this for a few years and wants to make my life as simple as possible to add, repair, or replace components as needed. My understanding is that if the heat exchanger between the inside and outside loops is sufficiently sized the efficiency loss in the exchanger will not be much different than the efficiency loss of using glycol throughout the whole system
2 -
-
I have an Arctic heat pump, and Spacepak fan coils (which are really just Phnix units from China). When I was shopping 3-4 years ago there wasn't as many options as there are today, but the Arctic has been running well. Their controls are not very good, I use a HBX heat pump controller instead of the factory controller. I'm guessing the Viessmann at least will have much better controls built in. I'm not thrilled on the Spacepak fan coils, the controls are also not very good and I have replaced two 24V transformers in the last 2 years…
If you are interested I have a bunch of videos on my system on Youtube, I did this DIY with some help from my local Arctic rep. Lots of learnings, but we are overall happy with how it all works.
https://www.youtube.com/playlist?list=PLl00MrbmZuKLKTqNBk_HueAszsW1A5CbQ
2 -
Indirect is not the best idea with a modcon and ever worst with an AWHP. Go for a heat pump water heater, takes up the same space, higher efficiency and cheaper.
The only reason I run an AWHP with an indirect is that I already had it. The big issue is recovery time and efficiency in the deep freeze. Come winter, I will need to add a resistance heater so I do not loose house heat for an hour or more during larger draws.
I was also doing some gardening during the recent heat wave here when the unit went into DHW mode. The nice cold breeze was nice, but that bit of cooling should really have been going to cool the house not the outdoors.
My thinking on plate HX with AWHP has changed over time and I'm now less against the idea. As long as you select a large enough one to have low approach temp and make sure the secondary flow rate is always bellow the primary flow rate, it should work well. Not over-pumping is the important bit because if the flow rate is too high, you are essentially mixing down the supply water with the return water which is bad for COP. Efficiency of an AWHP is all about SWT, so your design should always prioritize getting that as low as possible.
With a bit of care you can also run plain water and avoid any glycol or plate HX. This is what I ended up going with as it is much simpler.
0 -
the indirect can work but with a low temp heat source you have to size it to be a storage tank, don't size it way the manufacturers push as if it were acting like a tankless with the boiler output, size it like an electric were you have to have all the hw=eat you will need in the tank and it takes hours to recover. set a limit on the priority in the control
0 -
Read the warranty, I believe glycol or a couple freeze valves are required. I'm not sure freeze valves are a good option for cold climate however. Some units have the HX too low to use a freeze valve.
So glycol may be the safest for both freeze and warranty claims. I doubt a frozen HX would be a warranty item, and an expensive replacement.
Regardless of the DHW option with a buffer tank the glycol can be $$. A circ, valves and HX probably less than 500 bucks.
The newest A2WHP modulate pretty well and may not need more than 20 gallons of buffer. That makes the glycol option more reasonable.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I agree with @Kaos that DHW is a poor fit for AWHP. In addition to comfort issues in the heating season, you also have comfort issues in the cooling season. It saves no room in the mechanical room, saves no money in operating costs and costs a lot more to install compared to a HPWH. There's literally nothing to recommend it. Manufacturers offer them because installers expect them, but that's because they were trained on boilers.
To the question you asked: heat pumps have modulating compressors that can adjust the output based on the load, they operate best when they can run continuously with the output matched to the load. This works best when you have emitters that can modulate their output to the load, which is often doon with outdoor reset. In order for this all to work the heat pump has to be able to sense the amount of heat the emitters are drawing out of the water, the simplest way to do that is to have the heat pump connected directly to the emitters and use the return temperature of the water to sense how much heat is being requested.
If you put a heat exchanger between the emitters and the heat pump, in order to get it to work properly you have to have some way of letting the heat pump see how much heat is being requested. Heat exchangers are tricky in that if you don't have the same flow on both sides the heat transfer goes way down. The heat pump is modulating the flow of its circulator to match the output so you want to have some way of matching the circulator on the other side.
There's a reason most heat pumps are not installed with heat exchangers.
0 -
@DCContrarian - "The heat pump is modulating the flow of its circulator to match the output so you want to have some way of matching the circulator on the other side"
I don't know the details of the brands the OP is considering but my Arctic heat pump, in factory form, runs the pump at a constant speed 100% of the time. It is supposed to modulate the compressor in response to return water temp but the pump does not modulate. In this scenario it is relatively simple to balance heat exchanger flow.
What are people's thoughts on using an indirect water heater as a buffer tank for the heat pump and a heat exchanger to separate glycol in HP loop from water in indoor loop? I'm wondering how the heat transfer efficiency of an indirect compares to a properly sized flat plate HX.
0 -
"What are people's thoughts on using an indirect water heater as a buffer tank for the heat pump and a heat exchanger to separate glycol in HP loop from water in indoor loop? I'm wondering how the heat transfer efficiency of an indirect compares to a properly sized flat plate HX."
HP systems usually use water at a pretty low temperature. Let's say you want 105F leaving water, 85F return for the emitters. If you're feeding the emitters directly you just set the leaving water temp to 105F. You'd probably have to feed the buffer tank at at least 125F. Look at the performance charts and see the difference in efficiency, and more crucially, cold weather capacity, for 105F vs 125F leaving water temperature.
0 -
I think it depends also on the loads you are connecting to the HP. With zoned hydronics a buffer may be an advantage, although Enertech promotes a buffer tank less approach.
In cooling mode if you have a single air handler that is sized to the HP output, all is well. With hydronic heating that is zoned the HP may not ramp down low enough and you do not want it to short cycle.
As for HX, by far a FPHX outperforms a tank with coil. You can size a plate HX to a close approach design, A & B side within a few degrees. Using the FPHX design software is helpful if you go with a HX.
As always, pros and cons to glycol, both in SIM and HP. I like working with HX but you have some efficiency penalty and additional cost. So you need to look at the specific installation and weigh the pros and cons.
As for DHW, I would also want to know what is expected for temperature and capacity. DHW should be sized the same as a heat load is calculated. Some folks do fine with 40 even 30 gallons of DHW, yet others drain an 80 gallon tank.
When you use a HP to heat an efficient home and a HPWH you are cascading the HPS and the HPWH will operate at a bit lower COP than advertised.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
"With zoned hydronics a buffer may be an advantage, although Enertech promotes a buffer tank less approach."
I've come around to believing that a buffer is a necessary evil and you need to keep it as small as possible. There are two use cases: Most important, when the load is low you need some way to soak up capacity and keep the heat pump from short-cycling. In a zones system you have to be able to let the compressor finish a cycle when all the zones are closed. Also, in the winter if you can pull the heat needed for a defrost cycle out of a buffer it saves electricity versus having to use resistance heat.
So I'm not quite sure how Enertech does it.
0 -
I think a better way to think of a heat exchanger is a primary/secondary loop with a slight temperature drop. When you look at it this way, matching flows is not as critical except making sure that the secondary flow rate never exceeds the primary as I mentioned earlier. P/S piping does work with AWHP and the heat pump does pick up load properly and modulates accordingly (or at least mine does).
With a bit of careful design you can eliminate a buffer tank in most cases. The important bit is to have some zones that are always on or at least an aggressive outdoor reset. Defrost normally happens when there is a pretty decent heat load, so as long as you have the above, there will be some zones running. The heat for defrost would come from those zones. Since some zones will always be running, they will provide a decent volume of water and a base load to avoid cycling. This is the setup I run and I have had no issues with cycling except when I run radiant cooling, which is a story for another day.
If you do want a buffer, heat pumps do best with a series two port buffer. This doesn't have to be anything fancy, a simple small hot water tank with the element removed will do.
Trying to combine any type of indirect with AWHP sounds good in theory but it just costs you extra money and complexity. KISS is my moto.
0 -
"I think a better way to think of a heat exchanger is a primary/secondary loop with a slight temperature drop. When you look at it this way, matching flows is not as critical except making sure that the secondary flow rate never exceeds the primary as I mentioned earlier."
With a heat exchanger, the heat flow on one side always equals the heat flow on the other. The heat flow is the temperature change times the water flow. On the hot side, the exit temperature can't be less than the entering temperature on the cold side. On the cold side, the exit temperature can't be higher than the entering temperature on the hot side. So the theoretical maximum temperature delta, on either side, is the hot side entering temperature minus the cold side entering temperature.
Whichever side has the lower water flow will have the higher temperature delta, this can be as much as the theoretical maximum. The side with the higher water flow will have a somewhat lower delta. Since you want your emitters to be getting water at the output temperature you want the cold side — the emitter side — to have the lower flow. With a heat pump that modulates circulator flow I don't see how you guarantee that.
I'm still trying to wrap my head around the statement that the Arctic heat pump has modulating output but a constant speed circulator. To modulate output the temperature delta would have to vary, but since the heat pump can't really control what the emitters do it would have to raise the water temperature. I'm not sure that's something you really want.
0 -
OP Here,
Let me elaborate more on the situation….
The house is a 25 year old 2-story timber frame with structural insulated panels (SIPs) envelope. Very tight construction, exposed 1-1/2" exposed pine second floor, so the heat conducts pretty good to the second floor. We have a HRV. For the first 20 years, the only heat on the first and second floor was a 40MBU Jotul cast iron direct vent, standing pilot propane stove in the living room, which did a decent job of heating the house. We never run the burner on high because it would heat too fast locally, causing rapid cycling of the thermostat. We throttle the burner to an estimated 30MBU for slower steady heat.
The basement is 60% finished, the foundation walls have 2" foam insulation. The basement used to be heated by a small kerosene monitor. Five years ago we replaced the basement monitor with a 12MBU Mitsubishi ceiling mount split, and also added a 18MBU wall mount head in the 2nd floor hallway (open from first floor to roof). We also have a 30MBU Jotul gas stove in the basement, but only run that occasionally for ambiance.
DHW is from a 20-year old propane Rinnai tankless water heater.
We have 20KW of PE solar and currently cover 100% of our annual electricity (including heat/cool of a detached 1,700sf office heated by mini-splits).
We are nearing retirement and want to prepare the house for minimal overhead down the road as we intend to age in place. Efficiency / self sufficiency in the future is top priority. Installation cost now is not a big concern. Everything will be DIY.
GOAL #1: Get off fossil fuels. Propane is expensive and I have plenty of free solar electricity.
GOAL #2: DHW sucks. While the tankless can supply plenty of hot water, it takes minutes to get hot water to the second floor and we are fed up with eating the "cold water sandwich". The ability to add a recirc line is mandatory. I want to turn on a faucet and have hot water. Just two of us still at home, one regular shower. we are not bath people with the exception of the occasional bath for a grandchild.
GOAL #3: Supplement first floor heat to replace need to run gas stove. Will retain for ambiance only. Heat / cooling in the basement is fine via the mini-split. We don't use that space much anyway.
Second floor split adequately cools the second floor and the cold air spills down the open central stairway to the first floor, so we are OK there.
In heating season, the first and second floor are good if we run the gas stove, but it's about the most inefficient heating appliance you can imagine. It has no booster fan. Without it, The 2nd floor mini split can't quite push enough heat down to the first floor to keep up. Due to the construction, a first floor mini-split is not an option, nor are baseboard radiators or panel emitters. We do have room to install some Toester fan coils, both in toekick and recessed floor mounts.
on edit.. GOAL #4: As much as practical in a global economy, avoid products made in china.
0 -
While I love hydronics with the current state of the technology I would only recommend an AWHP if you intend to do floor heating.
Could you install an air handler in the basement with ductwork to serve the first floor and basement? Then the minisplit on the second floor serves that.
I still recommend a heat pump water heater. They don't work well with circulators either but you can plumb in a five gallon mini heater and circulate from that.
0 -
Maybe do a heat load calculation first, get a better idea of how many btu you actually need.
a basic electric water heater is an option if. It. Is just two of you in the home?
I don’t read that you have any Hydronics currently? If your option is small fan coils that need or more, a heat pump may not be the best option.
are you grid tied, do you have a good deal with the power company, at par perhaps? If so it seems staying all electric might be your best option, skip the hydronic is retrofits unless you can add some low temperature radiant.Invest in some thermal or battery storage to carry through the evening ifyou have a lot of PV. Or if your grid tie is a good option?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
This article explains how to estimate your heating load from fuel usage:
https://www.greenbuildingadvisor.com/article/replacing-a-furnace-or-boiler
This table shows heating and cooling design loads by county:
Those numbers will be necessary for any design discussion.
0 -
"Could you install an air handler in the basement with ductwork to serve the first floor and basement? Then the minisplit on the second floor serves that."
No room for air handler and / or ductwork. Basement is already well served by existing minisplit.
"This article explains how to estimate your heating load from fuel usage"
Propane tank serves Gas stoves, DHW, cooking, gas clothes dryer and Hot Dawg GFUH in detached garage. No way to separate out heating usage without installing sub-metering.
I have not done a heating load calc, and the high performance SIP building envelope makes the home easier to heat than typical. As mentioned, I do have empirical data: The first and second floor was heated comfortably for 20 years with just a 40MBU direct vent gas stove in the living room, turned down to well below 30MBU. The stove is only about 70% efficient, so I doubt we are getting more than 20-25MBTU into the space. We now have 18MBU of split system on the second floor. That single 18MBU head just about gets it done in heating season. We shut the gas stove off during the day when at work on all but the coldest days (less than 15F). We turn the gas stove on when at home because the first floor feels a tad chilly.
We also just replaced all windows and doors with modern high efficiency units.
"are you grid tied, do you have a good deal with the power company, at par perhaps?"
We are grid tied, and have 1:1 net metering for now. Our electricity is around $0.24/KWH. The utility is phasing out net metering. It sounds like we may be grandfathered in through 2040, but the future is unclear.
" I would only recommend an AWHP if you intend to do floor heating."
Why is that? I have room for four mini toekick/fancoils. The large ones are north of 8MBU each at 110/120 loop temperature. Floor radiant is not an option due to the finished basement. No space for emitter panels. No space for baseboards. But I can get PEX wherever I need to for Toesters.
0 -
The reason I would discourage AWHP is cost, everything is more expensive.
That said, if you just want to do four Toesters, here's what I would recommend: pipe the heat pump directly to the fan coils, no buffer tank, no zone valves. Let the water circulate continuously and attach your thermostats to the fans on the Toesters. If you have multi-speed fans, get a multi-stage thermostat so the fan speed depends on the heating load.
For this you want a heat pump that modulates the flow according to demand for heat. When there is no demand for heat — all the fans are off — flow will slow to a trickle.
This is the way a lot of AWHP are configured in Europe, it's very simple and relatively low cost.
Get a heat pump water heater for your hot water. Put a five gallon electric water heater downstream and run your circulator into that.
0 -
1500 bucks buys a simple 100% efficient modulating boiler, 10 Kw gives you 34,000btu/hr
You could be around 10 time that for a 3 ton HP and tank. Although the hp gives you a cooling option.
If you go with a hp, find a knowledgable installer\ service person. There is a lot of technology under the hood of the indoor and outdoor unit.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
If you're going to go all resistance you could just put in electric toe-kick heaters, they exist. Then the only installation cost would be running the wiring.
0 -
I would shop around a bit, air to water units are harder to find, but not that expensive if you can DIY.
I'm with @DCContrarian Install a simple direct to load setup with thermostats on the fans of the heaters. No buffer, no extra pumps, simple plumbing. You also will have very little volume so no need for a plate HX. I would still demo the ceiling of the basement a bit and at least install some floor heat for the bathrooms. These can be free running always ON zones, nobody complains if a bath is extra toasty. Too many issues with radiant cooling, stick to minisplits for that.
You can get 120F out of R32 units but they won't like it. 110F is a more reasonable number to shoot for, this will probably mean a couple of extra heater units with fans running at low speed. You won't be about to run much outdoor reset as nobody wants 90F air blowing at their feet.
0
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 113 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 110 Geothermal
- 161 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 998 Plumbing
- 6.3K Radiant Heating
- 391 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements