New Venting for 135-Unit Apartment Buildings
A community of a dozen six story 135-unit apartment buildings constructed in 1952 with one-pipe steam heating had an increase in uneven heat complaints.
Each building had two Pacific boilers, with a series of risers and a 200-foot long return to a vented receiver below basement floor level. Riser ends joined the returns with F & T traps, to feed the returns and vent the air through the receiver.
Those 200-foot returns looped around and under doorways. Over the years they lost their pitch and accumulated rust and scale. That blocked the free venting of air from the risers and mains to the receiver's vent.
The solution was to bypass the returns as a means of air venting and to add vents to the ends of the steam mains.
The problem was solved, and tenants are enjoying 558 radiators' improved heat distribution through faster venting.
Nice work!
Consulting2 -
Well if the returns are restricting air flow then they will obviously restrict the condensate return. Did you try and use rebuild kits at the F&T traps. The elements in the traps could have failed and you wont be able to get air passed it. Using the receiving tank to vent the system on a boiler feed system is a standard practice. All my 2-pipe steam systems have boiler feed tanks. those F&T traps look like they have never been opened
Time for my more or less standard comment, I guess… F&T traps are lousy main vents. Yes, they do have that thermostatic element which is supposed to act as an air vent and close when steam hits it. I know. But… I'd very much rather see real live vents. Use the F&T to keep the steam out of the return and, if necessary and you have the pressure, push the condensate uphill a bit.
- 117 Geothermal