I have a 1930s lake cottage with rolled copper tubing for the plumbing. A small 2" section of this tubing burst during a freeze. I removed the damage section but a new 1/2" coupler was too big by 1/16"-1/8" and 3/8" fittings were much too small. Were there variations in sizing back then? Do I need to crimp down both ends of a 1/2 piece of tubing to allow a good repair?

Comments

  • mattmia2
    mattmia2 Member Posts: 17,906

    what is the OD? there is tube size copper tube that is sized by the od and pipe size copper that is sized by the id. was you half inch coupler tube size or pipe size?

  • ChrisJ
    ChrisJ Member Posts: 17,623

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Intplm.
  • pecmsg
    pecmsg Member Posts: 7,442
    edited July 2025

    metric or refrigeration tubing (ACR) that goes by the outside dimension

    1/4 , 3/8, 1/2, 5/8, 3/4, 7/8 etc

  • kalisitiane
    kalisitiane Member Posts: 2

    Northern Wisconsin, so definitely a frozen pipe expansion and then a burst was possible. I'll put a caliper on the portion that's more interior and compare the two. Thanks for the input.

  • Larry Weingarten
    Larry Weingarten Member Posts: 4,185

    Hi, Sometimes silver solder is the simplest approach to burst tubing. I've repaired many frozen solar collectors this way.

    solar panel.JPG

    Yours, Larry

    pecmsgMad Dog_2
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,642

    Might be 3/8" TP pipe. Which is essentially brass, if I am not mistaken. Needs special adaptors.

  • Pumpguy
    Pumpguy Member Posts: 808

    Nominal rigid 1/2" copper tubing has an OD of 5/8". Many people don't understand the difference between nominal and actual.

    If you're dealing with rolled 1/2" copper tubing, it might in fact actually have a 1/2" OD.

    In any case, you'll need to know the actual OD before you can specify what fittings you need.

    Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
    Website: www.nashjenningspumps.com

    The first step in solving any problem is TO IDENTIFY THE PROBLEM.
  • mattmia2
    mattmia2 Member Posts: 17,906

    you can also use a swagging tool to expand one or the other to make them match up if it really is copper and really is between sizes.

    If it is some local standard brass size you can not expand it although you could expand copper to fit it.

  • retiredguy
    retiredguy Member Posts: 1,102
    edited July 2025

    Regular domestic water plumbing is measured by it's ID and refrigeration tubing is by OD. So, someone may have used 1/2" OD in lieu of 1/2"ID especially if that person was in the refrigeration or A/C business. Try going to a refrigeration supplier and buying couplers for 1/2"OD and see if that works. 1/2" copper for domestic water has an OD of 5/8" while 1/2" refrigeration tubing has an OD of 1/2". So, for example, 5/8" refrigeration tubing is the same as 1/2" nominal domestic water tubing. I said nominal since the actual ID of domestic water tubing changes with the grade of the tubing being M, L, or K, while the OD remains the same.

    Intplm.
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,716

    Silver braze the split closed. Simplest fix. Mad Dog

    SuperTechpecmsg
  • ChrisJ
    ChrisJ Member Posts: 17,623

    If he has 1/2" OD refrigeration tubing the 3/8" fitting he bought should have fit. The OD of refrigeration tubing and plumbing pipe is the same, the descriptions are different.

    At least that's been my experience.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 17,906

    except fittings sold as '3/8"' are typically tube size unless it is someplace that really knows plumbing.

  • Larry Weingarten
    Larry Weingarten Member Posts: 4,185

    Hi, I'll just throw it out there that some freezing in copper tube can expand the tube a little, so it is no longer the size of either plumbing or refrigeration tubing. So the choices are to either cut a bit more tubing out, back to where it didn't freeze, or silver braze/solder the leak. Finding a way to keep it from freezing in the first place would be nice, as soft copper can only be expanded so much… or maybe this is a good place for PEX. 🤔

    Yours, Larry

    PC7060
  • hot_rod
    hot_rod Member Posts: 28,078

    soft coil tube is not always perfectly round either, a bit of an oval shape from being coiled. So the OD might be a bit bigger, depending on where you measure.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream