Peerless Purefire
cody4422
cody4422 Member Posts: 4
Can anyone figure out why my Purefire makes banging noises while igniting. I have a video but site won’t allow me to download
  • Big Ed_4
    Big Ed_4 Member Posts: 3,241
    May need a cleaning and igniter ..
    EBEBRATT-Ed Member Posts: 18,248
    And a combustion test.
    SuperTechmattmia2
    HVACNUT Member Posts: 6,872
    When was the last time it was serviced?
  • EODagon
    EODagon Member Posts: 1
    Look at the swirl plate for signs of deterioration. And like EBEBRATT said definitely do a combustion test.
  • SuperTech
    SuperTech Member Posts: 2,614
    Could also be a venting issue. Any condensate looking in a horizontal section of the vent pipe will cause it. Maybe something nesting in the vent pipe. Could be poor condensate drainage. Most of the time it's either a bad igniter or the combustion isn't set up correctly. It's critical set the combustion up in minimum and maximum firing rate per the specifications in the installation manual.
  • cody4422
    thanks for the comments. It only happens when it’s cold. I am trying to find a Peerless pure fire boiler specialist
  • cody4422
    when the boiler is cold
    That boiler has one of the simpler interfaces. Get it running and compare combustion numbers to Peerless specs. Go from there.
  • cody4422
    why would it ignite ok when system is hot? already had someone here and they cleaned it and adjusted warming speed with no results
    mattmia2 Member Posts: 13,511
    more draft when it is hot. you have some sort of a combustion issue.