ADVICE/IDEAS NEEDED! 3 Commercial Hot Water Heaters
First post here, but a long time lurker!
I have an 80 room hotel which I operate & I typically like to do my own research to develop ideas/plan prior to engaging a plumber given I’ve seen the ‘easy route’ taken far too often. I also enjoy putting my best effort forth to make informed decisions, ones which make sense in the long run!
With all said, I am in process of getting my entire hot water system at this hotel overhauled/updated. While doing this I’d like to focus on how to make improvements with respect to flow, efficiency & longevity. Most want to just replace the equipment but using the same infrastructure/layout.
I have attached a sketch of my Mech. Room along with photos to supplement the detail provided below.
I will be going from (3) Rheem GN100-200 tank heaters to (2) new Rheem GHE100SU-200 tank heaters & (1) Rheem GN100-200 tank heater (reusing 1 old one)
Questions:
1) How much sense it would make for me to increase the existing 1.5” pipes (from the hot/cold trunk lines to water heaters) to 2”? How much GPM & Pressure increase should I expect?
2) Based on how the recirculating pumps are plumbed, should the hot lines be plumbed in a ‘Reverse Return’ configuration? Basically First In/Last Out (FILO)? Currently the system is piped to be First In/First Out (FIFO) & we have been going through hot water heaters/tanks every 6 years. I am convinced the current setup could be contributing to the short lifespan of these heaters.
3) Should the 2 return lines with the recirc pumps on them be tied into a different area of this system, where it will be more productive/efficient or are they good how they are? Biggest thing I am stumped about here is how one of the return lines enter into the room at 1" size then goes down to 3/4" and right before it goes into the cold water loop, reduces again down to 1/2", should I just redo all the piping to be 1/2" up until the 1" line coming into the room? Or instead do the opposite by upgrading all the 3/4" & 1/2" line to 1" throughout on this return feed?
4) This is my first time seeing 2 return lines. Could someone tell me what “setup” I may have so I can research more on this?
Feel free to chime in with any questions or suggestions if you see something concerning!
  • hotterthanhail
    hotterthanhail Member Posts: 4
    @Larry Weingarten no pressure fluctuations and GPM’s have already been calculated.
    To be clear, we have always had, at minimum, 2 (100 gallon) water heaters. Never ran out of hot water or issues with pressure.
    Only issue is that we can’t get them to last more than 6 years. While doing this changeout, I was wanting to make some changes/improvements to see how that fares us in respect to longevity, efficiency & overall use.
    mattmia2 Member Posts: 15,799
    Test the water chemistry, that will tell you what tanks will last the longest. Steel might be right for some chemistries, stainless for others.
    Mad Dog_2
  • tim smith
    tim smith Member Posts: 2,891
    I always prefer tanks & boiler. The most tried and true I have ever found was the AO Smith HW 300, 420 or 670 boiler & 2 - 119 gals tanks If 2 100s have done ok for you in past. I get 20 to 30 years at least usually out of this set up. Problem is its standard 80% combustion efficiency so you give up some energy savings for reliability. You also may not be able to go std efficiency depending on your states energy codes. I have found nothing that compares for cost of ownership to the above setup. Larry I'm sure is right about checking water chemistry, changing anodes and flushing regularly to increase tank style gas water heaters life.
    My .02 worth.
    Larry WeingartenPC7060
  • hotterthanhail
    Water Test from 2024 Uploaded. Performed by EcoLab. Let me know if you see anything here! Appreciate all the help.
    Our incoming water pressure floats between 40PSI-50PSI. Our main line coming into the building is 4" but once it hits the hot water heater room for cold water supply to the heaters, it reduces to down to 3".
    hot_rod Member Posts: 26,816
    you water is pretty hard, that will shorten tank life
    What is the hot water demand in gpm, that is how you size the piping?
    What temperature do you maintain?
    Tankless water heaters are very common in hotels now, for efficiency and continuous dhw
    If you go with a stainless tank or tankless you want to test for chlorides
    Is there a laundry on property ?
    Softening the hot water helps fixtures and soap consumption, also
    Larry WeingartenMad Dog_2
  • hotterthanhail
    @hot_rod
    Hot Water Demand average is 35GPM. Peak is closer to 57GPM, so would like to at 60GPM or higher, just to be safe when running high occupancy.
    140 degrees
    Thought long & hard about tankless. Really wanted it, but got scared should one go out 3-5 years in and that same model be discontinued, risking the replacement not being any to communicate with the others in series. Maybe one day, but not right now.
    There is laundry on property, the 1.5” hot line shown in sketch uploaded bypasses the mixing valve loop and goes directly to this area.
    I would like a softened on the entire water system, but two issues are:
    1. where my main feed comes in, I don’t have nearly enough space to put a proper system & have adequate space needed to service (average 3,500 gallons of water/day)
    2. A 4” head would kill the bank. Settling for just treating the hot side would let me get away with a 2” or 2.5” head. Much more manageable price. Will take something over nothing.
