Modbus RS485 chain question

We are setting up a system that has temperature control software to control a modulating gas valve through a Fuji temperature control unit and it has two wire RS485. We are creating a chain with three Invertek e3 VFD's that are 3 wire RS485. We feel we will have control issues with two wire and three wire communication in the same chain.
Two part question.
What are your thoughts and experience with this?
Second question, is there a work around like a usb hub combining two RS485 chains with slave 1-5 communicating on the same settings? Our software only allows communication to one rs485 usb chain on one com port with one usb plug.
Comments
-
I don't think you'll have any trouble with it, but you never know. There are rs-485 to Ethernet converters, a pair of those should isolate the segments at the cost of more complexity and additional cabling.
0 -
RS-485 is a three wire network and it can go thousands of feet if done right. Using it as 2 wire assumes a common ground is present that has no voltage offset between the two (or more) pieces of equipment. There are various ways to provide isolation if the ground is an issue.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 116 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 107 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 983 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements