Cold water is hot due to amateur plumbing

steam-rookie
steam-rookie Member Posts: 131

the hot water tank in the photo is being used for storage only. The coil in the boiler still works, and produces plenty of hot water. All of a sudden, out of nowhere, the cold water is mixing with the hot water. I am getting hot water from all of the cold water taps

in the house.The current set up has been like that for many years. I have been told on numerous occasions that the pump is in the wrong place. I have been told it should be on the top somewhere.
so, looking at the photos. Can anyone tell what is wrong and why I am getting mixing with the Hot Water into the cold taps.

73 year old one pipe system with original American standard boiler, oil fired becket, 2 inch steel pipe main, 100 feet long, with 8 radiators above.

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,409
    edited May 3

    Check valve missing

    Screenshot 2025-05-03 at 10.38.44 AM.png

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • neilc
    neilc Member Posts: 3,024
    edited May 3

    is the recirc running?

    does it have a check?

    and or is it stuck open?

    yeah, nevermind, still need a check on the cold supply to the domestic hot

    known to beat dead horses
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,100
    edited May 3

    You have a cross-connection somewhere. The usual suspects...

    1. Single handle mixing valves like shower bodies, Washing Machine valves.
    2. Mop Sink connections that are altered.
    3. Domestic hot water coils using a globe valve to blend.

    Yes, you also may need a check valve, but when this condition "suddenly" occurs, it's usually at the aforementioned locations. Mad Dog

    EBEBRATT-EdLarry WeingartenPC7060
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,710

    Agree with @Mad Dog_2 if the problem just started a check valve may not be the fix.

  • steam-rookie
    steam-rookie Member Posts: 131

    thank you for the quick reply.

    There used to be a check valve just after the pump where the red valve is located. It caused a lot of water hammer when the washer went on, so I took it off. The only other thing that has changed that I think of is that the heat is off. Anyway, I think installing a check valve at the new suggested location looks like something I could try. I like that idea because it’s way closer to where it seems like it’s mixing to me.
    that pipe coming down should be ice cold. It’s pretty much hot all the way up now. Maybe placing the check valve there might be a really good idea.

    hopefully when we run the washing machine there won’t be a lot of banging

    73 year old one pipe system with original American standard boiler, oil fired becket, 2 inch steel pipe main, 100 feet long, with 8 radiators above.
  • neilc
    neilc Member Posts: 3,024
    edited May 4

    if you innstall the check on the feed to the DHW, you might / will need an expansion tank on the hot side since the DHW will be isolated from expanding back to the house side,

    and what Ed Mad Dog says, Cross Connections ?

    known to beat dead horses
  • mattmia2
    mattmia2 Member Posts: 12,618

    I was about to say that then looked at it more closely and i think the check is just on the bypass, the dhw system is still open to the cold water inlet through the coil.

  • steam-rookie
    steam-rookie Member Posts: 131

    I believe that the last comment made is correct.
    The check valve should be on that cold water inlet.

    if it starts to have water hammer I also agree about the expansion tank. There has never been an expansion tank anywhere

    That will be my next question without a doubt.

    73 year old one pipe system with original American standard boiler, oil fired becket, 2 inch steel pipe main, 100 feet long, with 8 radiators above.
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,409
    edited 11:41AM

    I also agree that using the check valve will require an expansion tank like this one: https://www.supplyhouse.com/Amtrol-140N43-THERM-X-TROL-ST-5-Expansion-Tank-3714000-p

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?