Boiler for infloor heating

plumbit
plumbit Member Posts: 16

got a quote for a boiler for a two large zones of infloor heating.
One option is a Laars FT 301

And the other is a navien NFB301c

What is the better boiler option?

Comments

  • Ironman
    Ironman Member Posts: 7,716

    The Laars is the better boiler, but the installer is 95% of the equation.
    Focus on finding the best HYDRONIC contractor that you can.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    GroundUp
  • GroundUp
    GroundUp Member Posts: 2,347

    100% agree with Bob above. Even the best boiler can perform poorly with an improper install and/or setup, but the Laars is a better boiler in my opinion as well. With that said, I'd sooner have a well installed Navien than a poorly installed Laars and the same can be said for support. If one or the other contractor is not local to you or doesn't perform service, the other may be a better option regardless of brand. Side note: how large is this space that requires such a large boiler?

  • plumbit
    plumbit Member Posts: 16

    what are things to look out for?

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,710

    The contractor is the most important thing and you can do better than a Navien.

    Ask them for references of the work they have done.

    Are they getting permits if required?

    Will they install everything in accordance with the MFG requirements?

    How many service technicians do they have that are familiar with the equipment?

  • hot_rod
    hot_rod Member Posts: 25,020

    how large are these two zones?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • plumbit
    plumbit Member Posts: 16

    one is 6500 sqft and the other is 1000

  • Kaos
    Kaos Member Posts: 617

    7500 sqft of floor heat can do about 150kBTU at a reasonable floor temp. 400kBTU boiler is a bit overkill…

  • hot_rod
    hot_rod Member Posts: 25,020

    any other loads? Seems like twice the boiler than what you need

    IMG_0314.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream