question about a Burnham V904A
Asking for myself as a fellow is using this boiler to replace a Van Wert VA1400 steamer coal stoker with a single 4 inch riser and no drop header.
Apparently they are welding a second connection to the exposed pipe in the image and
I have no idea where the piping would end-perhaps in the side tapping in section 3 of the boiler?
Where would the skim port be located on a BurnhamV904A boiler be located?
The drawing on page 11 of the manual make no mention of it or the location for the Hartford Loop tapping.
Comments
-
Its all in the manual. Pg 38 I think. See attached
0 -
Here's the manual:
The return goes into the tapping in the rear. That side tapping might be for a condensate loop.
The V-904A only needs one 4" riser to a 4" header. It looks like that riser goes to an existing header, and the equalizer drops towards the rear. This should be fine as long as the pipe sizes and pitches are good.
0 -
Thank you both, I had not waddled down through the manual looking for the piping layouts yet when I posed the question to the forum.
0