does anyone know of a company that makes replacement a coils with metal drain pans, instead of plastic? I need to replace a 41 year old 3 ton r22 coil that sits on top of an oil furnace. Most of the time I try to install these at least 4” above the furnace. Due to space limitations on this job, I may only be able to get it 2 to 3” above the furnace. I was thinking a metal pan may be better. Thanks to all.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,798

    CRC- Coil replacement Company may have what you need.

    zepfan
  • pecmsg
    pecmsg Member Posts: 6,079

    A translation to raise the coil up at least 6” is required on oil furnaces.

    zepfan
  • HVACNUT
    HVACNUT Member Posts: 6,769

    A 41 year old R22 system?

    I guess any 410A coil wouldn't fit, regardless.

    Is there room on the return for a downflow 410A evaporator with duct modifications. Filter rack upstream.

  • SuperTech
    SuperTech Member Posts: 2,584

    Any coils with a metal drain pan that I see are at least 20-30 years old, and super rusty. A plastic drain pan with adequate space between the furnace will work just fine providing that the limit switch on the furnace is operating correctly.

  • pecmsg
    pecmsg Member Posts: 6,079

    on the return WILL rust out the furnace heat exchanger.

    SuperTech
  • zepfan
    zepfan Member Posts: 426

    thanks to all that responded. The CRC company while very helpful only make custom built coils, which would not be cost effective for a residential replacement. I think what I am going to do is buy automotive heat shield panels that have adhesive backing. I think I can get a general replacement A coil about 3” above the furnace. The heat shield that comes in 12” x 12” squares I am going to cut it and line the top of the transition and bottom of the pan with it. It says it protects to 2000 degrees, so It should work to protect the pan.
    yes the system is a 2.5 ton 41 year old R22 unit. The crazy part is that another company replaced the furnace 5 years ago, but left the ac and coil in service. Otherwise I would replace everything and start over.