One pipe steam dry return blockage

How can I clear the partial blockage in my return ? A past repair was made by connecting a by-pass 3/4 " pipe at the furthest point in the loop (by means of a clamped saddle over a drilled hole in the return) and running it back to the main loop pipe at the boiler. This 3/4" alternate return pipe has "gone cold" , and so the need for a clearing of the original return or replacement of either the original or alternate returns. I would really appreciate your sage advise on this one ! Thanks, Art
Comments
-
Usually the only parts that will really clog are the wet returns. Whatever is in a main extension can usually be flushed out with a hose if some sort of debris gets in there.
Both of those conditions are pretty rare, usually it is an issue with sagging pipe and water trapped somewhere because of the sag or a problem with venting.
2 -
Thanks alot for your quick reply! There was a significant blockage in the lowest wet part of the return at the base of the boiler that got repiped. But the water level in the boiler at the sight glass seems to be slow to recover , particularly when the boiler is firing alot during really cold spells.
0 -
Tell us more about the water level.
Where does it start?
How quickly does it drop during a call for heat?
How much does it drop?
How long in minutes after the call for heat ends does the level return?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
-
That stoppage was below the water line, so that is not considered a dry return. I've never seen a stoppage in a dry return. Mad Dog
1 -
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 425 Carbon Monoxide Awareness
- 108 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 961 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements