Slant Fin B200
L_I_John
L_I_John Member Posts: 1
edited April 2025 in THE MAIN WALL
My B200 keep timing out with the error codes A01 or A02. I have to keep resetting it. No one knows what the problem is. What can I take out and replace it with?
e it with. It has 5 zones.
    109A_5 Member Posts: 3,963
    edited April 2025
    Were these things checked ?
    https://s3.amazonaws.com/s3.supplyhouse.com/manuals/1282657809967/37801_PROD_FILE.pdf
    Also understanding where the unsuccessful ignition and/or loss of flame happens in the operation sequence may help.
    EBEBRATT-Ed Member Posts: 20,151
    @L_I-John
    You don't throw away a perfectly good boiler because it won't run. If the technicians can't find the problem its because they haven't looked.
    Check "find a contractor" on this site
    And post your location we may know someone that can help.
    Are you on Long Island?
    Also if the gas valve seems to randomly close or just not open, The 120V section of the Argus PHC794-S1 control board could have a failing solder joint and/or relay.