Monoflo system

Hello all.. Got a question about adding new, additional baseboard (fintube) radiator to an existing monoflo system. Customer is building a new room addition on the house so needs an additional radiator.
My issue is that I don't have a lot of linear piping to work with on the main loop in the basement to add 2 more monoflo tee's and have them spaced far enough apart from each other. If I did this and kept all the existing tee's as they are, I only have about 4 feet of linear piping on the main loop to work with. I understand how water flows thru a monoflo system, flowing thru path of least resistance. And that is another issue. Because the new room addition and new radiator will have a long run of 3/4" piping… Longer than I want. But there isn't much other choice. It will be about 14 feet of 3/4 piping out to a 10 foot radiator, and then 14 feet back to the main..
So my question is, what is the best way to do this?
Would it be an option to instead connect the new radiator to an existing radiator in the adjacent room using the existing monoflo tee's? This would obviously make the total length of piping/rads longer and create more resistance to flow.
Or would it be better to just add 2 additional monoflo tee's for the new radiator? But like I said, I only have about 4 feet of piping to work with on the main basement loop.
Could another option be to install a valve on the 1 1/4 main loop between the tee's and adjust valve to control flow?
Any thoughts will be greatly appreciated. Thank you
Comments
-
Monoflo systems are… twitchy. If it were mine to play with, I'd take your last opeiong — basically pipe your new radiator by T ingoff the existing pipe cand running out to and back from the new radiator, and putting a valve on the existing pipe between the takeoff for the new radiator and the return. Now as a bit of extra flair, you could make that valve a zone valve and set it up with a thermostat in the new space, but "reverese acting" — that is, when the new space needed heat, you'd have the valve close. You could do that with a relay very neatly to reverse the action of the thermostat.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Why wouldn't you add a seperate zone for this new addition? Leave the monoflo zone alone. Mad Dog
4 -
Better to be able to have independent control of the addition's heat. Mad Dog
3 -
You didn't specify if the main is 3/4 or larger. If it is 3/4, you certainly should NOT add any additional monoflo tees otherwise you'll be installing a larger pump. 3/4 is marginal on any monoflo system.
Follow the advice of Mad Dog and install a new zone for the new room. Leave well enough alone with the existing monoflo.
2 -
-
-
-
If you take the time to research how to properly design a Monoflo® tee system by selecting the proper size diverter tee from this Monoflow Design Guide in order to determine the actual pipe sizing needed and if you require one or two diverter tees on that particular radiator and how that will affect the remainder of the radiators on the system, you will ultimately make the determination that a separate zone is more efficient and a better use of your time in properly designing an alteration to the existing "working" design that is already there.
Or you could guess and hope for the best!
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
The main loop is 1 1/4"
0 -
I didn't want to make the system zoned… It is currently a single zone system. So to make it zoned I'd have to also change some of the main piping at the boiler as well..
And also the new room addition is on the far side of home from where the boiler is. Zoning is just a lot of extra piping work and controls/pump/ect. that the customer simply can't afford
0 -
How many emitters presently?
What size takeoffs for those emitters ?
What pump is presently installed?
You'll have to do the math to see if you can sneak in an additional emitter.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
There are currently 7 radiators total. ( new room will make 8 )
They are all 3/4" directly off of the 1 1/4" main.
I'm not certain what pump is currently installed, but I'm pretty sure it's a Taco ecm variable speed circulator.
0 -
You can try adding another rad. If the branches are long you may want a Monoflow tee on the supply and return. May or may not work. The extra resistance of the Monoflow tees may cause a problem
There is another way that will not screw up the Monoflow system. Cut in two standard tees into the Mnoflow main 1 1/4 X 3/4" and feed the radiator off that. In one of the pipes supply or return install a small circulator to feed the new radiator. Control both circulators of the same thermostat. Put a balancing valve on the radiator feed to control flow.
By using two standard tees the Monoflow system will work as before. Regular tees will not restrict the Monoflow loop like Monoflow tees will
1 -
Excellent.
I'm sure you can add another radiator to a 1 1/4 system without compromising the flow rate to any significant degree.
Just to be sure………………
Get the system running for at least 30 minutes. Measure the supply temp and the return temp with an infrared gun (put some black tape on the copper). Provided the DT is not excessive (greater than 20F or so), you'll be fine with the additional rad.
FWIW, I have struggled with a monoflo with 3/4" piping and I could not get the DT below 25 even with a Taco 11 pump. The six monoflo tees coupled with the 3/4" piping was an exercise in futility.
0
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 966 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements