pex for fewed/return on boiler line.

retired17
retired17 Member Posts: 18

Has anyone ever mixed existing copper lines with oxygen pex on a boiler feed and return?

If you did is the pressure the same?

thanks

Comments

  • mattmia2
    mattmia2 Member Posts: 12,800

    you mean oxygen barrier pex? look at the id of the pex and the copper. the nominal sizes aren't the same especially in larger sizes. you need to use more like 1" pex to get the same id as 3/4" copper pipe. also pex that large gets very hard to work with unless you buy it in straight sections and use fittings like it were copper.

  • Big Ed_4
    Big Ed_4 Member Posts: 3,210

    Question is not clear …

    There was an error rendering this rich post.

  • retired17
    retired17 Member Posts: 18

    so its oxygen barrier orange pex. I was tring to ask if I could run a 1 inch oxygen barrier pex for a 10 foot section of boiler feed and or boiler return pipe instead of copper.

  • Jamie Hall
    Jamie Hall Member Posts: 26,014

    Hot water, I presume? Well… see the above comments for sizing. There are two other considerations: both lines will need to be well supported, preferably in a trough, as PEX gets flexible at higher temperatures and, if not supported, will sag. Also, there is a definite high temperature limit. You won't likely reach the rated temperature — typically around 100 F — but it's something to consider…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • retired17
    retired17 Member Posts: 18

    thanks jamie.