radiator fittings
retired17
retired17 Member Posts: 18
so I am soldering some tees from the boiler to the radiator pipes. the tees they sent me are wrong. should have been 1 1/4 x 1 1/4 x 3/4, instead they sent 1 1/4 x 3/4 x 1 1/4.
if I use the 1 1/4 x 3/4 x 1 1/4 and have the back end of the tee to the radiator, will it make any differance in the pressure?
thank you
Gary
    mattmia2 Member Posts: 16,852
    can you draw it or at least use words like branch and run? in hot water it usually doesn't make a lot of difference unless you are pushing the flow limits or are right near a circulator or a few other controls.
  • retired17
    going from the boiler through the pump about 6 feet toward a radiator branch.
    you could put it at the corner so the tee acts as the ell at the corner
    or you could do this with an offset
    PC7060
  • PC7060
    PC7060 Member Posts: 1,809
    where did you by the part? Supply house will ship out replacement same day if their error. Otherwise Matt’s suggestion of placement at border is good one.
    EBEBRATT-Ed Member Posts: 20,207
    If your putting in a bunch of tees your going to have more resistance using the tees you bought. Flow through a tee at 90 degrees is more resistance than a 90 degree elbow of the same size as it is a sharper turn. Will it make a difference? For 1 or two tees probably not for a bunch of them it could.
    You have to name the tees correctly. If the main runs straight through the tee and the branch going to the rad the tee is a 1 1/4 x 1 1/4 x 3/4 tee although some refer to it as a 1 1/4 x 3/4 tee.
    The tees they sent you are 1 1/4 x 3/4 x 1 1/4
    You name the run connections first starting with the largest pipe size and name the branch last
  • retired17
    thank you for your comments they were helpful