so I am soldering some tees from the boiler to the radiator pipes. the tees they sent me are wrong. should have been 1 1/4 x 1 1/4 x 3/4, instead they sent 1 1/4 x 3/4 x 1 1/4.

if I use the 1 1/4 x 3/4 x 1 1/4 and have the back end of the tee to the radiator, will it make any differance in the pressure?

thank you

Gary

Comments

  • mattmia2
    mattmia2 Posts: 18,399

    can you draw it or at least use words like branch and run? in hot water it usually doesn't make a lot of difference unless you are pushing the flow limits or are right near a circulator or a few other controls.

  • retired17
    retired17 Posts: 18

    going from the boiler through the pump about 6 feet toward a radiator branch.

    20250409_203937.jpg
  • mattmia2
    mattmia2 Posts: 18,399

    you could put it at the corner so the tee acts as the ell at the corner

    or you could do this with an offset

    image.png
    PC7060
  • PC7060
    PC7060 Posts: 1,980

    where did you by the part? Supply house will ship out replacement same day if their error. Otherwise Matt’s suggestion of placement at border is good one.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    If your putting in a bunch of tees your going to have more resistance using the tees you bought. Flow through a tee at 90 degrees is more resistance than a 90 degree elbow of the same size as it is a sharper turn. Will it make a difference? For 1 or two tees probably not for a bunch of them it could.

    You have to name the tees correctly. If the main runs straight through the tee and the branch going to the rad the tee is a 1 1/4 x 1 1/4 x 3/4 tee although some refer to it as a 1 1/4 x 3/4 tee.

    The tees they sent you are 1 1/4 x 3/4 x 1 1/4

    You name the run connections first starting with the largest pipe size and name the branch last

    mattmia2
  • retired17
    retired17 Posts: 18

    thank you for your comments they were helpful