I assume this is no bueno
Options
TheStressMachine
Member Posts: 50
Comments
-
Forgot to mention exhaust piping is nice and sealed so no leakage in the house, CO detectors sit above any gas appliance I have.
0 -
-
-
-
-
Is this natural or LP gas?
If the number is out of spec, then the heat exchanger probably needs cleaning and a combustion analysis done.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
If my limited understanding of combustion is correct, you can get the same O2(electronic analyzers convert O2 to CO2) percent with too little air or excess air. If you are on the too little air side you are making a lot of CO so you could get good CO2 numbers but still have it wrong.
0