Switching relay
I have an Greenstar combi 100 p / 151p zwb28-3a. … zwb42-3a. I have 2 circular zones.. Can I use the Taco SR502-4. And if so do use a jumper to the ZC ZR
KEITH
Not enough information, the Taco SR502-4 may not be 100 % compatible with an existing system.
If nothing (jumper or other equipment) is connected to the ZC ZR terminals the circulators the SR502-4 is controlling will never run.
One Pipe System1 -
The jumper should be factory installed, and you would leave it. XX dry contacts to the thermostat connection on the boiler.
Here is a wiring example with a Caleffi ZSR
120V power, lower left
thermostats on top
XX to boiler contacts, usually a TT connection
The newest version has a snap in removable 40Va transformer, circuit breaker protected
What if the proprietary OEM control equipment was used, just replacing the CZM100 with a switching relay may not be enough to restore proper operation. And the third party controls don't seem to control zoned circulators AND zone valves if both were used. Again not enough information was presented.
One Pipe System0 -
This is actually two different boilers. The manual has both models on the cover because it is for both boilers. Do you know which one you have? it will be on the rating plate with the serial number. It is a good thing to know for future reference.
thank you for your time on this. I’ll find out
@109A_5 has a good point about the third party control compared to the recommended control. This boiler has DHW priority built into the onboard computer software. The means the Domestic Hot Water for taking a shower will use the full capacity of the burners in order to make sure you have enough hot water while you are in the shower. The space heating (or central heating CH) will stop operating for the short time that you are using the hot water. The Taco Control may not communicate with the GreenStar and keep the circulators operating for the zones without regards to the DHW operation.
I would look into the CZM100 control and see if that is reasonable priced compared to the Taco SR 502.
Here is the circulator 2 Zone option from the IO manual for your heater
the CZM 100 is no longer available. Whats the comparison to it. Is there a Taco that’s compatible
Keith
thank you for your responses. I neglected to give you more information. The Greenstar Combi 100p/151p ZWB42-3A23 S3124 model 7-738 100-611
Thank you
Keith
Since it appears the CZM100 uses a proprietary communications method with the boiler and the thermostats. You would have to verify (inventory) this and all the equipment that needs to interact. Since the system control method may have to change. It appears the boiler will except more conventional control for space heating.
With abandoning the CZM100 the thermostat(s) may have to be replaced too.
Really need the 'Big Picture' to make a good and realistic recommendation.
One Pipe System0 -
I found cmz100 thank you for your time