Switching relay

I have an Greenstar combi 100 p / 151p zwb28-3a. … zwb42-3a. I have 2 circular zones.. Can I use the Taco SR502-4. And if so do use a jumper to the ZC ZR
KEITH
Comments
-
Not enough information, the Taco SR502-4 may not be 100 % compatible with an existing system.
If nothing (jumper or other equipment) is connected to the ZC ZR terminals the circulators the SR502-4 is controlling will never run.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
The jumper should be factory installed, and you would leave it. XX dry contacts to the thermostat connection on the boiler.
0 -
Here is a wiring example with a Caleffi ZSR
120V power, lower left
thermostats on top
XX to boiler contacts, usually a TT connection
The newest version has a snap in removable 40Va transformer, circuit breaker protected
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
What if the proprietary OEM control equipment was used, just replacing the CZM100 with a switching relay may not be enough to restore proper operation. And the third party controls don't seem to control zoned circulators AND zone valves if both were used. Again not enough information was presented.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
I have an Greenstar combi 100 p / 151p zwb28-3a. … zwb42-3a.
This is actually two different boilers. The manual has both models on the cover because it is for both boilers. Do you know which one you have? it will be on the rating plate with the serial number. It is a good thing to know for future reference.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
thank you for your time on this. I’ll find out
0 -
@109A_5 has a good point about the third party control compared to the recommended control. This boiler has DHW priority built into the onboard computer software. The means the Domestic Hot Water for taking a shower will use the full capacity of the burners in order to make sure you have enough hot water while you are in the shower. The space heating (or central heating CH) will stop operating for the short time that you are using the hot water. The Taco Control may not communicate with the GreenStar and keep the circulators operating for the zones without regards to the DHW operation.
I would look into the CZM100 control and see if that is reasonable priced compared to the Taco SR 502.
Here is the circulator 2 Zone option from the IO manual for your heater
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 106 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 104 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 952 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements