Foamy / Dirty Water in sight glass, Loud Panting Radiators Again

IanMac227
IanMac227 Member Posts: 12

Hello All,

I've posted on here before about a loud "breathing or panting" sound coming from all of my radiators (alternating whistling release and suction immediately after). I went through the whole system, making sure everything was sloped right, boiler pressuretrol setup correctly, vents on the radiators were good. The only problem I still have are the pipes immediately after the boiler not angled correctly, which I can't change right now. The mains slope correctly on either side after that initial portion.

At one point I changed and increased the venting off the mains. Now I have a mixture of new Gorton and Maid o Mist Number 1s. This seemed to help a lot for a while, there was still some noise but it wasn't enough to be disruptive. But now all of a sudden the noise is back with vengeance. I pulled all the main vents and cleaned them. They appear to be working fine, although I only confirmed that by blowing through them. I'm not sure if there is a better test.

I did notice the water in my sight glass is dirty when running and also has some foam on the top (pic below). It looks like there is some rust contamination on the top as well. Is it possible I'm making bad steam or have too much contamination? It was serviced last fall but I don't believe it was skimmed or flushed. Any help would be appreciated! We have to wear ear plugs to sleep right now unfortunately.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 7,456

    I don't like to see suds in the gauge glass, but that may or may not be related to your problem.

    Why is the water level so low?

    It's possible that your water is involved, but really only if the water level is dropping dramatically and rapidly when the boiler is steaming. That's why I ask about the water level. If your level is up where it should be then when the boiler makes steam it plunges to where it is now, that water is going into your main pipes and causing trouble.

    Or maybe you are just hearing the normal sounds of a loud vent. I can't hear it from here. Have you tried a different, maybe smaller vent on your radiator to see if anything changes?

    Or it could be the common occurrence of house settling having created a low spot in the supply pipe to that radiator and the steam is collapsing when it hits that cool water at the start of a call for heat.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Big Ed_4
    Big Ed_4 Member Posts: 3,149

    My first thought is the steam production is lower then needed to fill system .. I would recommend replacing the loss of supply pipe insulation before increasing firing rate ..

    There was an error rendering this rich post.

    techforlife
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,320

    Water is dirty. Needs a good cleaning

    mattmia2techforlife
  • ChrisJ
    ChrisJ Member Posts: 16,554

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,483

    Skim it and check the PH

    techforlife
  • IanMac227
    IanMac227 Member Posts: 12

    The water level does vary a bit throughout the whole cycle. The picture I took was a little bit into it, but when off the water level is slightly above halfway up the sight glass. The lowest I typically see is just above the bottom of the sight glass.

    The sound seems to be coming from all the radiators. Most are 4s and 5s plus a couple 6s that are the furthest away from the boiler. Nothing has changed in that setup and everything seemed to be working great a few weeks ago like that. I can certainly try to go smaller on the bigger ones. I also cleaned all of them except a few I replaced (a few months ago).

    I haven't been able to find any low spots but I will check again tonight. I haven't confirmed the pH or skimmed yet as well.

  • Big Ed_4
    Big Ed_4 Member Posts: 3,149

    The " breathing or panting " …. The head of steam is slipping back …

    There was an error rendering this rich post.

  • ChrisJ
    ChrisJ Member Posts: 16,554

    All of my vents breath like this. In my system I believe it's the steam "inch worming" down the mains as the warm up. Steam pushes forward into the cool piping and condenses, sucking more steam into the space, over and over.

    For now I'd concentrate on skimming your boiler and getting the water nice and clean. After that we'll see how it goes.

    Do you have an accessible skim port, and do you know how to skim?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    techforlife
  • Big Ed_4
    Big Ed_4 Member Posts: 3,149

    I agree with skimming , Just thinking there is more to this story :)

    There was an error rendering this rich post.

  • ethicalpaul
    ethicalpaul Member Posts: 7,456
    edited March 4

    The lowest I typically see is just above the bottom of the sight glass.

    This should not happen, you are surging. Skimming is the prescription. Don't blame the pH. Once your water is good and staying good you can put the pH at 10 or so and be loving life with clean water.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    techforlife
  • IanMac227
    IanMac227 Member Posts: 12

    Thanks everyone. I will try to skim it this weekend and see what type of difference it makes. I've lived here less than a year so I don't know the whole history of this boiler but the tag on it says it hasn't been skimmed in 5 years. Not sure if this needs to be done more often.

    techforlife
  • ethicalpaul
    ethicalpaul Member Posts: 7,456

    No, normally you would never need to skim unless you introduced oils into the system with new piping, etc.

    But skimming is easy and the right way to clear floating stuff. And you'll basically get a boiler flush for free afterward when you lower the water level back down.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Member Posts: 12,200

    With the foam and age my bet would be on priming rather than surging. Try draining a good portion of the water out and adding fresh and see if the water stops foaming an exiting the boiler.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,483

    Put some of the boiler water in your wife's brand new saucepan and put it on the stove to see how it boils. That may tell you something

  • mattmia2
    mattmia2 Member Posts: 12,200
  • ethicalpaul
    ethicalpaul Member Posts: 7,456

    What is the difference between priming and surging? Aren't they two names for bubbles forming during boiling and then that bubbly water exiting the boiler with the steam?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Member Posts: 12,200

    Surging is the steam violently exiting the surface of the water because something like a layer of oil is blocking its exit usually taking slugs of water with it. Priming is the water forming a foam with the steam and that foam being pushed in to the mains.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,483

    Surging is usually oil or dirt and muck

    Priming is usually caused by PH

    mattmia2
  • Big Ed_4
    Big Ed_4 Member Posts: 3,149

    I wonder if any " skimming n the can " like Squick was added to the system .. Could any cause foaming ?

    There was an error rendering this rich post.

  • pedmec
    pedmec Member Posts: 1,185

    Your water quality is terrible. You can't make quality steam with dirty water. Flush the boiler and then refill. Don't worry about adding fresh water. Its only a one time thing.

    ethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 7,456
    edited March 6

    you guys haven’t watched my video where I put oil in my boiler. There are no slugs of water, there is just like similar to when milk boils over on the stove

    Has anyone seen a slug of water? Where does the idea come from? Honest question!

    or the one where I dumped in way too much 8-way with zero surging or priming

    Squick doesn’t seem to cause surging. It’s mostly that bituminous earth powder that ties up any oils.

    Cutting oil added to boiler:

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Member Posts: 12,200

    the episode of the galloping gourmet where he is heating water with lard on top of it and it blow up in his face. when i have tried to melt butter in the microwave too quickly.

    we have seen people with lots of additive i their boiler with the water leaving the boiler that stopped doing that when they drained it out and put fresh water in the boiler.

    ethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 7,456

    Thanks. Yes, if you put additive into dirty water it can surge. But at least 8-way, if you put it into clean water, it causes no harm, even way too much

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • ethicalpaul
    ethicalpaul Member Posts: 7,456
    edited March 6

    Thanks Ed. If we accept those definitions, what is the difference between them as far as behavior? Do they both result in a significant water line drop? Do they both cause water to enter the mains and possibly radiator runouts?

    This article has a lot of these terms, but they all seem to be saying the same thing to me: https://www.lenntech.com/applications/process/boiler/foaming-priming.htm

    Priming, Surging, Carryover, Foaming, Wet Steam, they all seem to be saying the same thing—a reduction in surface tension of the water that allows bubbles to form and be carried along with the steam into the main, taking a lot of water out of the boiler.

    This article has even more terms including Churning and Percolating! https://calray.nyc/what-is-surging-in-a-boiler-and-why-is-it-dangerous/#:~:text=Boiler%20surging%20is%20sometimes%20also,boiler%20surging%20is%20also%20noisy.

    I especially like that one because I have expressed surging in terms of a coffee percolator that purposely carries water up a tube to pour over the coffee grounds repeatedly. Imagine a coffee percolator being an overfired boiler with zero header height.

    Also interestingly, this article, and others I have seen blame LOW pH for surging! Here on this forum people think high pH causes it, which I have not been able to repeat experimentally.

    However, there are other causes of boiler surging as well:

    Oil leaks that infiltrate the boiler water

    Lack of filtration on the water supply

    Low water pH (acidic) due to failure to treat boiler water

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • techforlife
    techforlife Member Posts: 120

    Skim first and ask questions later. It's only sensible.