Circulators with IFC internal flow checks, some discovery.
hot_rod
hot_rod Member Posts: 27,415
I built this clear pump display to try and observe the small spring checks in action. The IFC fit right into the discharge of the circulators. They have a low "pop" pressure, around 1/2" psi.
First off you want to have some sort of strainer, filter, dirt separator in the piping. It doesn't take much more than a grain of sand to hold them open. See the particles on the paper towel.
On my first run I had some of the clear plastic machinings in the piping and it held the check completely open immediately.
Next the pump and circuit needs to be 100% air free. On first start the air entrained in the fluid would cause the check to bounce, flutter, chatter, pick a word. In this short demo loop it took less than a minute for the air separator to clean the fluid of all air. The check operated smoothly from then on.
Troubleshooters tell me they have replaced these damaged checks after 3-5 years of service. I suspect the checks chatter themselves to an early death.
The check is in a turbulent condition this close to the impeller. Most any check manufacturer asks for several pipe diameters distance between a pump discharge and the check.
All in all, properly protected and commissioned I do see the value in these spring type, conical seal type of checks in circulators.
Screenshot 2025-02-28 at 2.22.24 PM.png Screenshot 2025-02-28 at 2.24.12 PM.png
GGrossmattmia2HydronicMikeDJDrewtechforlifeSuperTech
  • GGross
    GGross Member Posts: 1,877
    Well you get to have all the fun huh?
    Larry Weingarten
    mattmia2 Member Posts: 16,688
    If someone was getting ghost flow, the ifc failing would be one of the last things I would think of but apparently it should be the first.
    Alan (California Radiant) Forbeshot_rodtechforlife
  • GroundUp
    GroundUp Member Posts: 2,513
    Well darn it, now I want a clear poly volute
    PC7060Alan (California Radiant) Forbes
  • jumper
    jumper Member Posts: 2,534
    Should have known that it was too good to be true.
    back to zone valves?
    The weighted flo-checks are pretty durable and effective. A large enough piece of crud could hold them open a bit also.
    I like the spring type hydronic checks, they are a bubble-free seal. The key is keeping the fluid clean. But this applies to balance valves, thermostatic valves, really any device in the fluid stream.
  • tim smith
    tim smith Member Posts: 2,932
    one of the main failure points we found with IFCs. The plastic pin that slides back and forth through pin hole would vibrate enough over few years and cause a groove in pin which would hang up and not allow to close.
  • It doesn't happen very often. And it takes awhile to figure out the culprit.