Safgard 1150 LWCO question

My brother in law called me for no heat on his oil fired boiler. There was no power to the burner and I traced it back to the LWCO, a Safgard 1150. The yellow low water light was on but the boiler showed about 10lbs of pressure with the temperature below 70F, so I think he's got enough water over the boiler.
I jumped out the cutout and the boiler fired. I ran it a few minutes while I looked up the manual for the Safgard and the yellow light on the Safgard went out, so I removed the jumper.
I didn't remove the sensor because I didn't have any tools on me save for my meter, but my question is whether the sensors in the cutoffs go bad or if they need any kind of periodic cleaning. I left him with heat and the LWCO in place but I know if it tripped once it's either bad or there's low water (no leaks found).
Ideas? Thanks.
Comments
-
-
0
-
But don't use pipe dope or tape on the probe when you put it back in. It must have a good ground connection from the probe to the boiler and thence to building ground.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
As long as you know that the water content is appropriate, since it is a hydronic boiler, replace the entire LWCO. Steam can dirty up the probe but unlikely on hydronics. Electronics get intermittently unreliable all the time.
0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements