Any device to prevent high wind from blowing out the WH pilot light?
Jells
Jells Member Posts: 649
I have a Smith Proline tank WH that vents to a brick flue on the top floor of a building. Maybe 4-5 ft of 4" duct and the chimney rises maybe 3' above the roof. I used to have a Minitherm boiler there that would get whatever that safety sensor is called get tripped in high wind. I got rid of it more than a decade ago and replaced it with a tank (tiny apartment), and all was good. but last spring I changed the WH and now 2x this winter the tenant has called to say the WH is out.
Is there anything to be done? Any kind of flue damper than can be used with a simple atmospheric tank? Seems unlikely, but I'm asking.
    mattmia2 Member Posts: 16,745
    the draft hood
    if it was tripping the spill switch on the old boiler you have to figure out your vent issue.
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,093
    edited February 2025
    Hi, One approach is to increase the size of the standing pilot. The other is to understand what really happens when it's windy. You would want to be there, watch the pilot, feel around the draft hood, feel any breezes coming into the room, see if operating other equipment has an effect on the pilot… Diagnosing the problem could take some effort, but can be an interesting exercise in building science 🤠 Then there is figuring out the best way to fix the airflow. Could be as simple as a new vent cap… but I've had good luck increasing pilot size 😉
    Yours, Larry
    Intplm.
  • Jells
    Obviously it's a vent issue, If I could figure it out on my own I would not be asking here!
    @Larry Weingarten unfortunately it is not my residence, it's a rental. I can't be living there waiting for a wind event!
    Talk to me about chimney caps. There are none. This is an old school 4 stack chimney.
    Jamie Hall Member Posts: 27,357
    A chimney cap is dead simple. Just a flat metal plate or sometimes a cone, slightly larger than the diameter of the flue where it exits the chimney, held up on metal standoffs (on old chimneys it would have been a stone slab held up on a brick or two at each corner!) just far enough for the side openings to be greater than the flue area by a factor of two or so. Simple. Works wonders if the top of the chimney is too close to the roof, as yours likely is.
    tcassano87
  • Jells
    Ok. How does it work to break whatever is going on? Is the problem a venturi effect when the wind blows across the flue top?
    the wind blows down the vent. the cap deflects it around the vent
  • Jells
    So here's the chimney. The one on the left is the culprit. I looked at the caps on the market and there's a flabbergasting variety. What would be most appropriate?
    Have the mason you get to fix the cap put a masonry one on. That chimney has other serious issues.
    Is that on the outside of the building so it is exposed to the cold of outside all the way up on 3 sides?
    That building next to it that is much taller isn't helping matters.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,530
    With the unit up on the top floor venting into the top of the stone chimney and surrounded with other buildings.
    I am thinking of two solutions ,
    "H" type termination on the top of the chimney ….
    Or a pilot relight kit …
  • Jells
    What exactly is a masonry cap and why can't I DIY it? When I google "masonry chimney cap" I get some variant of this. A few holes drilled in the bluestone top, some caulk and some Tapcons should mount it, no?
    The chimney is flush with the outer wall of the building, interior on 3 sides, and the building next door is 50' away.
    i mean i'm pretty sure the cap is just going to fall off on the roof if you try to drill a hole in it.
    plus if you don't fix the cap you're going to be replacing the whole part of the chimney exposed to freezing temps
    Well, thats the geometry anyway, though I'd put the cap lower. But I don't like the idea of drilling into that existing cap. I'd much rather see a nice slab of bluestone the size of the top of the chimney and perhaps an inch thick, supported on spacers, two brick high, at each corner and halfway along the sides… A competent mason using high quality grout can do that — and it won't crack anything (further than it is!) and I'd be rather surprised if it blew off…
  • Larry Weingarten
    Hi, One more thing. I'm not seeing the 4" metal vent that the water heater is hooked up to. I'd want it brought all the way up to the top of the masonry or a bit higher so the water heater had a better chance of creating a natural draft. This would need to be under a hood so no rainwater could get in. Also, best if it's double walled, so it retains heat (and draft) better.
    Yours, Larry
  • PC7060
    PC7060 Member Posts: 1,804
    The cracked stone on chimney is allowing water into the brick and need to be addressed. Get a chimney mason to replace the stone with a masonry crown. They could also fit flue caps.
  • Intplm.
    Intplm. Member Posts: 3,013
    @Jells You will need to have your chimney repaired. Currential draft, direct draft down the chimney are surely occurring. One thing that may also be happening is wind blowing into the sides of the chimney where holes and cracks probably are, causing the water heater to shut down.
    From the looks of it in your pictures the chimney has been repaired before and needs it again.
  • ChrisJ
    ChrisJ Member Posts: 17,373
    For what it's worth the house I grew up in had an atmospheric furnace and a water heater that fed into a masonary chimney. Over 40 years the pilot never blew out in either of them and there was no cover on the chimney.
    The chimney extended above the ridge of the roof by 3 feet or so, and then the terracotta clay extended a few inches above the brick.
    So what, why am I saying that?
    Apparently that arrangement works under most conditions. And I think it was already previously mentioned, but the draft hood should prevent such problems. I'd patch up that chimney and fix the leaks etc because they are going to bite you over time and it's going to be bad, but I suspect you're going after the wrong thing. Like you said, the previous tank was fine for years.
    I'd pull the cover off of the heater and look at the pilot to make sure it's burning good and it looks like a reasonable sized flame etc.
    PC7060Larry Weingarten
  • Jells
    Thanks Chris, tou have a great point that the previous WH didn't blow out. The flame looked fine to me, but perhaps increasing it might be the best 1st step. I will get some masonry caulk and seal the broken bluestone, but this place is at least 125 years old, solid, and going nowhere till it's torn down after I'm gone. The lot is worth more than the building by far.
    I was hesitating to respond to all the apocalyptic comments and assumptions about the chimney. These are extremely common around here, and many if not most do not have covers. I looked on Google Earth and can see many, many open chimneys. There's no holes in the chimney as suggested, the outside wall of the building is parged. I've had 2 masons up there in recent years, one repaired the parging and one rebuilt the brick parapets before the new roof and coping went on, and neither commented about the chimney.
    There's never been draft issues with the vent pipes terminating inside the chimney wall, this is how all the units here were when I bought it, and how subsequent heating contractors did it when they updated various units. All the units have CO detectors and I've never had any go off.