Drip to nowhere.
Hmm. Looks like this drip goes to a drain. Sink is directly below.
I can say with absolute certainty it does NOT go back to the boiler. Wonder how much water loss this would account for. Pipe is riser for a single rad. 1-1/4".
Main is lagged pipe in the lower left corner of the bottom picture.
Thoughts?
If that pipe with the drip on it isn't the main than what is it?
Riser to 2nd floor rad.
Here's the bizarre main connection.
Maybe it was a steam supply for laundry equipment or a water heater. It isn't really in the right place to be a drip, it is both coming off the side of the lateral above the condensate and is on the uphill end of the slope of the lateral.
Did this leak come from a source above the pipes in the pictures? And not from the pipes? Or maybe its a leak from both?
If it really is a drip from that riser and radiator, it could be a lot. Not hard to calculate — take the EDR of the radiator, multiply by 0.24 and that will be the pounds of water per hour of operation.
Who knows. Building is from 1912 and we've owned it since the early 60s.
So not since our ownership. It does look like it had been repaired more recently than the original installation. Partly done in galvanized for one.
Maybe because of the downstream horizontal union?
Are you saying that you have not been able to find the end of the pipe? Or, does it go down through the floor? and if through the floor you don't know where it goes?
Is there evidence that one some time wet returns were under the floor? Sometimes, the get replaced with new wet returns running on top of the floor.Dave in Quad Cities, America
http://grandviewdavenport.com0 -
No evidence there were ever under the floor wet returns. This is the only drip in an otherwise conventional one pipe system.
I have to open up more wall to see where it ends. Being in line with the sink drain raises suspicions.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.1 -
Gets warm, not steam hot. The takeoff on the tee is angled slightly downward so some condensate may be going that way.
If it ends in a drip loop to the sanitary drain I'm thinking of just capping it off. What would it be there for anyway?
The takeoff from the main is weird too. Why all the s turns instead of tee-nipple-45 like everywhere else?
if it were hooked to the sewer, unless there is a water seal at the bottom, it would be able to vent and would get steam hot. and you'd lose a ton of water through it as steam.
It doesn't, so I'm figuring there's a loop seal lower down.
See any downside to just capping it?
Are you sure there is no radiator connection being all drips i have ever seen or installed where on the bottom not piped off the side being for it to serve its intended purpose it would be facing down not to the side being on its side a decent amount of condensate would need to build up before draining . Why not just use a camera and look down the wall or better yet just remove the rest of he damage dry wall and visually take a look ? At one tome there may have been a wall or ceiling mounted rad but in which case there would be a wet return for condensate to drip too one would assume .
peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating3 -
If it were me, I would have my hammer in hand, plus a prybar, a small saw to cut the lath, and the shop vac to clean up the mess. Get busy and tear into that wall. No amount of guessing is ever going to come up with the answer of where that pipe goest and does it do anything. My guess is that it runs down the wall a ways and then is simiply capped off. Maybe it was used for something at sometime in the past, but my guess is that it is presently doing nothing at all. On the other hand, if it is connected to something…. or disappears under the floor, you need to deal with it and the sooner the better. This is not going to be a big project, just a minor annoyance and you will be so happy once the riddle is solved.
Keep us posted, these riddles are great fun.
http://grandviewdavenport.com1 -
This is a put your hands in your pockets until you understand what is going on situation. it could be steam to something that was removed, it could be knuckelheading. it could be something else we didn't even think of. what does the plaster look like below it, does it look like it was patched or there was something mounted there? remember automatic storage water heaters and any of the laundry equipment we have now or even they my grandparents used didn't exist in 1912. i know solid fuel kettles were common for heating laundry and water, something steam for heating a kettle or a drying cabinet or for ironing is certainly possible.
- 87K THE MAIN WALL
- 58 Biomass
- 113 Chimneys & Flues
- 109 Geothermal
- 161 Indoor-Air Quality
- 995 Plumbing
- 391 Solar
- 55 Water Quality
- 45 Industry Classes
