equalizing tanks?
![dave_126](https://secure.gravatar.com/avatar/2f9b04b0b89d871c0c7d995e14769bb1/?default=https%3A%2F%2Fvanillicon.com%2F94a12a1ae90e9e7b4e737527fdbb40f6_200.png&rating=g&size=200)
I have a house that has 2 boilers with 2 tanks. One tank goes to each boiler, with an equalizing line between the 2 tanks. The boilers have a common return. 1 tank runs out of oil before the other tank gets to 1/4. The equalizer line isn't plugged so why aren't the tanks the same level? Should the line be before the filter?
Comments
-
-
-
The equalizer pipe between the tanks is probably plugged.
Did it ever work or is this something new?
It would be better if each boiler returned to the same tank it pulls from.
Does the common return go to the tank that runs empty or (more likely) the tank that has more oil in it.
Do the suction lines go gravity feed to each boiler independently
0 -
Impractical install. Small orifices in fire valves should be replaced by full port ball valves. Equalizing line between tanks should be 1/2" minimum, UNFILTERED, I.E., No restrictions for tank equalization. Install filters after that. Whoever installed this was overthinking and obviously inexperienced in oil heat reliability.
1 -
For reference, here is our install, with ball valves and equalizer before the filters.
0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 100 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 101 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements