Residential Steam Boiler Replacement - EDR Questions
Itzyklein
Itzyklein Member Posts: 16
edited February 23 in Strictly Steam
Hi guys!
I’m a newbie to steam heating and boilers and I have some questions about replacing a gas fired steam boiler
A few years ago we bought a 4 Family house in Brooklyn, NY. its approx. 3200 sq ft, there’s 2 apartments on each floor and the basement is used for storage. The boiler is almost 40 years old, its a 245K BTU Burnham, (See images below)
I called my tech at the beginning of this season to service the boiler, and he told me that it has a crack and will need to be replaced in the near future. Over the last few months, it has been losing water and constantly needs to be refilled. I asked my tech for a quote for a replacement, which he provided.
Before I go ahead with the replacement, I want to make sure that it will be done correctly the first time around
I have spent some time on this site reading and watching videos and have learned a lot from it, thank you guys!
My questions are;
  1. Near boiler piping - is a Must, I will make sure that it is included
  2. Isolation valves to perform a yearly cleaning (King valve, return valve, mud leg drain valve) This isn’t currently included. Do I need this in my system, should I request it?
  3. Clean and skim. There is no mention of this in his quote. What do you recommend?
  4. Chimney - the quote says that it doesn’t include Chimney lining or cap. I’m not quiet sure what that is or if I need it.
  5. Boiler size - the quote is for a 238K Williamson, though the radiators weren’t measured
  6. What else is important?
Also, I would like to get a quote from another heating company that has experience with steam systems, the “Find a Heating Contractor” tool on the website has many options, are there any specific contractors that you would recommend for my situation?
Thanks for taking the time to read and respond
IK
«1
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,509
    Number 3 and number five are instant disqualifications. Boiler must be skimmed, and the only correct way to size the boiler is by measuring radiators.
    Personally, I am not a big fan of king valves. Just one more thing to go wrong. Rather than coming up with all sorts of creative means to pressure bomb the sludge out of the boiler, it is preferable and possible to avoid the sludge in the first place.
    ethicalpaulGrallertItzyklein
  • STEAM DOCTOR
    Definitely a good idea to have the chimney inspected and lined if necessary. And to have a chimney Cap added if necessary. But typically that's not the job of the boiler company. Will typically be done as a separate job by a chimney company
    ethicalpaulItzyklein
  • STEAM DOCTOR
    And just to back up a bit. Are you certain that the boiler is actually leaking? Easy way to check is to fill the boiler above the top of the boiler, and see if any water comes leaking down onto the burners
    Itzyklein
  • STEAM DOCTOR
    You might want to think about replacing the wet returns. Not critical or vital but something to consider.
  • KC_Jones
    KC_Jones Member Posts: 5,907
    Need to measure all the radiators for sizing. DO NOT SKIP THAT PART. The contractor is 100% guessing if they don't measure. It's easy to do if you'd like to complete the task on your own, we are happy to help.
    Valves, I wouldn't worry about king valves, I'd make sure they included valves at any low point so you can flush things out if needed, I think that is more important.
    Skimming is a relatively easy task if you'd like to take it on yourself, what is important is that they install the skim pipe so the skimming can actually happen. That is very important no matter who does the work.
    If you have concerns about the chimney, contact a chimney company and have it inspected and see if they recommend having it lined. If I was guessing, they will suggest it needs lined.
    Make sure the quote says they will do the piping to manufacturers specification, including proper pipe size. The pipe size is important. The one they quoted needs 3" header, we see on here frequently that they don't like going over 2" piping, don't let that happen. Of course we don't even know if the quoted boiler is the right size.
    I am not familiar with NY geography to know 100% which contractors would serve your area, but I'm pretty sure there are several good ones that to Brooklyn. Others may chime in on that.
    2014 Weil Mclain EG-40
    ethicalpaulSTEAM DOCTORdabrakemanItzyklein
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,806
    Steam Doctor's the doctor; what he says is 100%.
    Asking a Brooklyn boiler salesman if you need a boiler is akin to asking a Brooklyn barber if you need a haircut.
    If this guy wouldn't size the boiler by measuring the radiators, I wouldn't be sure your boiler's leaking.
    How much water are you adding weekly? (How many inches in the sight glass?)
    Itzyklein
  • AdmiralYoda
    AdmiralYoda Member Posts: 737
    The good news is that there are a few well respected pro's on this site that service your area. I'm sure they will chime in soon.
    100% agree with @STEAM DOCTOR
    Itzyklein
    ethicalpaul Member Posts: 8,141
  • Grallert
    Grallert Member Posts: 1,030
    Also, go to the books store here on this sight and get "we've got steam heat". I think that's the name of the book. You will want to become knowledgeable on you steam system it will save you headaches and money.
    STEAM DOCTORItzyklein
  • delcrossv
    delcrossv Member Posts: 2,189
    edited February 11
    @JohnNY for one.
    I don't mind king valves, but more important is easy access to the mudleg.
    If your guy gave you a quote without measuring the rads, you can take him right off your list.
    mattmia2 Member Posts: 15,573
    also @EzzyT and @clammy
    delcrossv
  • dabrakeman
    dabrakeman Member Posts: 868
    Everything @KC_Jones said plus do the mamual fill test on your boiler to make sure it is actually the boiler itself that is leaking (not a return line or leaky vents...).
    If you have been on this forum you are probably familiar with the radiator edr estimating tables. If not ask. See that 628sqft number on your boiler plate? That should match up to the total edr of your radiators. Ideally it may be 5-10% less. You should do this sizing yourself so you know. Nonetheless, a qualified steam guy would do it anyway rather than just basing off your existing boiler.
    Itzyklein
  • Itzyklein
    Thank you
    That is an interesting point you make, I didnt consider otherwise, based on the amount of water that needs to added and the age of the boiler.
    I will try test you mentioned
  • Itzyklein
    I dont have a clear amount but the low water cutoff is kicking in and turning off the boiler, then the automatic feeder kicks and the boiler comes back on a short while later. When I add a few inches of water in the sight glass within a few days its back to the low water cutoff kicking in
  • Itzyklein
    I'm aware that the near boiler piping is crucial, I didnt realize how important it is to measure all the radiators. I'll look around this site to learn how to do that on my own.
    I see both @STEAM DOCTOR and @KC_Jones discourage putting in a king valve. How do you avoid a buildup of sludge?
    Regarding the skimming, I think I will ask whoever is doing the replacement to take care of that
    edited February 12
    You add a little 8-way product to your boiler water in order to increase the pH which dramatically reduces the amount of corrosion that occurs.
    And you absolutely minimize the amount of fresh water entering your boiler (from things such as blow-downs and leaks), but that should go without saying.
    ItzykleinSTEAM DOCTOR
    I would start with the symptoms and that someone told you it needed to replaced when you call one of the NYC contractors, have them diagnose it first rather than asking for a replacement. It could be a return leaking somewhere where you can't see it or condensate that is delayed in returning to the boiler or water getting thrown in to the mains from the boiler and tripping the lwco.
    There can be other places besides the boiler for leaks and there can be system issues that cause the water to leave the boiler and trip the lwco.
    If you fill the boiler to the mark on the sight glass while it is off, if you check it over a couple days(or hours if it is leaking a lot) during the off cycle, does the water level fall?
    CLamb
  • Itzyklein
    Hi
    I did the test and got confirmation
    I opened the water supply to the boiler and watched the level rise in the sight glass. As the level reach the top of the sight glass I heard water dripping and saw it pouring out over the burners
    I lowered the water level to the higher black line on the sight glass and fired up the boiler. I went to the roof and saw clouds of steam coming out of the chimney. Within an hour the water level was so low that the LWCO turn off the boiler until the feeder topped it up
    Looks like it's time to replace?
    yes, new boiler time.
    STEAM DOCTORneilc
  • New Hampshire DIYer
    New Hampshire DIYer Member Posts: 27
    I own a 4200 sq ft house that includes a 900 sf apartment. I had our leaky gas-fired steam boiler replaced about 8 years ago after reading lots of advice on this site. The Strictly Steam professionals on HH.com are amazing. When I did the radiation calculation I found that I could cut the size of the boiler by fully one third.
    One other thing I've found super useful is a VXT automatic water feeder because it has a water meter and display so you know exactly how much water is going into your boiler over time. This is in place of the usual stock feeder. I didn't want an errant leak to go unnoticed and end up adding lots of oxygen rich make-up water. Finally, I always use one or two Steamaster tablets once a season after refilling after blowing it down. The label on the bottle recommends more tablets but my boiler only takes about 7 gallons of water.
    Good luck!
    Slant/Fin TR-40 w Carlin EZ-Gas burner. 3" riser into 3" drop header. Two 2.5" mains: 43' and 25' serving 11 radiators w/ EDR of 585. 3200 sq ft 1850s Greek Revival house in Concord NH - 7478 avg degree days.
    BobC
    you can take the jacket and probably the flue collector off or look up with a camera or mirror to confirm it is leaking somewhere in the heat exchanger, there is a small possibility that a connection of some sort is leaking but if a section or joint between sections is leaking it is unlikely to be worth the labor to repair that if it is even repairable vs replacing the boiler
  • random12345
    random12345 Member Posts: 504
    Post pics of the front and sides of all your radiators. Measure dimensions: height from floor, width, length along the top not including the thickness of the endcaps, and center-to-center distance between each section. Writing/symbols are helpful to identify manufacturer.
    Itzyklein
    It is very likely a hole rusted in a section. it can't hurt to take the jacket off and confirm that but i'd be surprised if it wasn't.
    Itzyklein
  • Itzyklein
    Yeah, I started measuring and taking pics of all the rads to calculate EDR
    The building has a total of 15 radiators, most are the same type. I'll post here when I have all the measurements and pics
  • JUGHNE
    JUGHNE Member Posts: 11,513
    Can you show all the piping on the boiler, floor to ceiling, all sides?
    How about your main steam air vents also?
  • tcassano87
    tcassano87 Member Posts: 99
    I’m a plumber in NYC in queens, see far too often guys around here just go off the size that was originally there. 100% have someone who measures and check all the rads as well as the near boiler piping and the main in the basement before deciding on a size and brand. I install, but personally don’t size them, if you’re looking for a trustworthy company in BK or the general area feel free to message me
  • HeatingHelp.com
    HeatingHelp.com Member, Moderator, Administrator Posts: 194
    @tcassano87, you should sign up for our Find a Contractor listings. Thanks.
    Forum Moderator
    tcassano87ethicalpaulCLamb
  • Itzyklein
    Hi all,
    Thanks so much for your advice so far, I've learned so much from this chat and from browsing around other chats and articles
    I measured all my radiators in the building, we have a total of 16. Most are the same type, and then a few odd ones as follows:
    12 radiators are the old style column radiators, all are the same depth and height (3 columns = 9 inch deep, and 38 inch high) They vary between 4-7 sections per radiator to a total of 69 sections between all the radiators. The charts say 5 EDR per column. That comes to 345 EDR so far
    IMG20250216171017.jpg IMG20250216171116.jpg IMG20250216171059.jpg IMG20250216171059.jpg
  • Itzyklein
    edited February 23
    Then we have 3 recessed / enclosed radiators. Inside they seem to have 4 tubes with fins. I need help to identify them and figure out their EDR. They are all 6 inches deep and 5.5 tall (measured from the bottom of the radiator, not from the floor) they are about 28 wide
    I don't know what this type of radiator is called or what its EDR ratings are
  • Itzyklein
    The last radiator is the odd one out, it has 4 tubes, is 6 inches deep and 30 inches high with 10 sections, the height doesn't match up with the charts and I can't make out any of the markings on it
    IMG20250221152333.jpg IMG20250221152224.jpg IMG20250221152231.jpg IMG20250221152234.jpg IMG20250221152239.jpg IMG20250221152325.jpg
  • Long Beach Ed
    edited February 23
    The cast iron convector elements are similar to the ones I linked below sold today by OCS.
    https://ocsind.com/wp-content/uploads/2016/05/15981-OCS-Catalog.Updated15-11.pdf
    Your 28" ones are about 26 sq. ft. of EDR each.
    Maybe someone can offer a more precise rating, but this should be a close estimate.
    ethicalpaulItzykleinLRCCBJ
  • KC_Jones
    I can't find that exact one in the charts either, but based on ones that are close I'd go 3 per section, so 30 for that one. If the entire house was filled with them I'd advocate for digging deeper, but one radiator isn't going to throw things off that much. Add that 30 to the 26 per recessed convector and I get 453 total.
    In the Williamson line that would put you exactly at the GSA-175, you got quoted the GSA-238 which is 2 sizes bigger, do not let them install this, it's far too big. They sized off the old one, which is totally wrong.
    ethicalpaulItzykleinSTEAM DOCTORbburd
  • Itzyklein
    Whoa! 2 sizes too big!!
    My estimated calculation also came to about 450.
    The mains in the basement are about 80 feet long and are not insulated, neither are any of the risers or returns. Do we need account any additional EDR for those?
  • STEAM DOCTOR
    edited February 24
    As they say in Brooklyn, oei vei ( I think that the spelling may vary slightly, depending on which part of Brooklyn you are in). Definitely do not oversize. And even more importantly, don't hire someone who does not know how to size the boiler. Feel free to give me a buzz.
    LRCCBJ
    Steamhead Member Posts: 18,197
    Consulting
    I looked here and found one that was very close:
    https://www.heatinghelp.com/assets/documents/American-Radiators.pdf
    Use the 4-tube Corto chart. Their version is 32 inches tall and 35 square feet. ISTR that the National Aero rads that were 30 inches tall had the same EDR as the 32-inch Cortos.
    Consulting
    No, there is already a 33% built-in "markup" for piping which is already too much.
  • random12345
    The 4 tube rad is 3.5 sq. ft./section x 10 sections = 35 sq ft.
    https://babel.hathitrust.org/cgi/pt?id=mdp.39015035429805&view=2up&seq=1713&size=175&q1=r174-40
    It was a standardized size. It's too bad the writing around the top plug is hard to make out. I would have liked to have been able to identify it. There were a couple of manufacturers that made 30" tall rads. National Radiator made the Aero, and Columbia made the McKeesport. I thought it looked very similar to a Thatcher Gothic, but the legs aren't consistent with that and height is too short…mystery. Maybe if you took a picture of the other side, the writing would be clearer? Won't change the EDR though.
    I agree with you about the column rads. If they are all 3 column, 38" tall, then it's 5 sq. ft/section. If you can take a pic of the clearest writing around the bottom you can find, that would help identify if you're curious. See below.
    As for the convectors, if you want the most exact ratings, I would need to know the manufacturer. Otherwise it's just an approximation, which might be good enough. Take a look underneath, top and sides of each convector with your phone camera for any writing. The cabinet may also have writing/identifying marks. Possibly behind the grille too. If you come up empty, I'll have to guesstimate.
    I think those column rads were made by Republic Radiator Co., but they are standard units so any standard 3-column chart will do.
    Consulting
    STEAM DOCTORrandom12345
