Minimum Temp with 4Way Mixing Valve?
Cyclist77
Cyclist77 Member Posts: 259
What is a realistic minimum temp I can send out to a radiant manifold with a 4 way mixing valve on a CI boiler?
    hot_rod Member Posts: 27,413
    looking at this cutaway view of a mix valve, if the vane was rotated left, the return temperature would just circulate back out. The controller could open the valve any amount to get a temperature mix up, as long as it has a supply of warmer water. So the lowest temperature would be the return temperature.
    With an actuator and control, the ODR curve could start the mixed temperature at any point
    70 degree SWT on a 70 degree ambient is where this example starts
  • Cyclist77
    Thank you. I am beginning to get my head around this.
    The reason I ask is the shoulder seasons. Currently we use our "scorched air", I love this description!, during these seasons. Then we start up the boiler when cold weather settles in.
  • Cyclist77
    Is it possible to have the maximum temperature in a CI boiler set below 180F when running a radiant floor heat system? If so what is the lowest it can be safely set?