Small DIY radiant bath heat
Jmichael
Jmichael Member Posts: 6
Hello folks,
When I built my house 20 years ago I was going to do underfloor heat. I piped 2nd floor with oxygen barrier pex. I also did my Primary bath encased in 2" mortar covered with granite. I then discovered Geothermal from a friend and changed to that because of the complexity of in-floor and ease of install of Geo. So here 20 years later I have a cold bath floor. Its still plumbed for radiant. Could I run the small single loop from my hot water heater with a mini type system or is it similar cost to do a small are verses large area? I came across the Taco radiant mixing block, which could be the answer if not for the price. I can live with floors as is, I just new there was a genius here to tell me what is possible.
Regards, Mike
    hot_rod Member Posts: 26,563
    A small electric water heater can work well for a small room. It may be less $$ than a HX block?
    With the small 6 gallon tank, you can select the element wattage. They come with around a 1300- 1650W 120V, but you can downsize to slow down the cycling.
    Mad Dog_2GGrossJmichaelmattmia2
  • Jmichael
    Thanks for the answer, the cost of the mixing block is about $2000.00. It does everything with just 4 connections, that's why it looked interesting. What would be approx. cost of systems you show?
  • GroundUp
    GroundUp Member Posts: 2,464
    The mixing block doesn't do everything. You still need an air eliminator, expansion tank, purge valve(s), etc so if you have the space, I'd agree with Bob that a standalone water heater would be a better option financially than the mixing block. The tanks are only a few hundred dollars and can be purchased at any big box home improvement store
    Mad Dog_2GGrossGrallert
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,381
    Keep it very simple....Mad Dog
    To be honest I didn't put expansion tanks on those small systems.
    8 gallons of water going from 65°- 100°= .0048 X 8G= .0384 g of expanded water
    Fill it to 5 psi, it may go up less than 10psi. With a 30lb relief you have plenty of room.
    If you use just the T+P in the tank, at 150 psi you have a lot of safety room.
    LWC is another piece that could be eliminated, the heater has a temperature safety. I used a lwc if the heater was above the piping.
    A manual air vent on top of the tank is sufficient also.
    It's fairly easy to find scratch and dent small heaters at plumbing wholesalers or big box stores. $150, or 1/2 of new price typically.
    You need.
    Tank
    Pump
    T&P gauge
    Webstone dual purge valve
    Setpoint control, use a digital like Ranco or Johnson Controls, Honeywell, etc.
    Mics fittings
    Depending on where you shop 500 bucks or less
    Too bad you can't find these Laing units anymore. The heater, pump, temperature and safeties were all built in. You could literally connect the pex in and out of them.
    Jmichael
  • Jmichael
    Hot_rod
    The Laing unit sounds like the Taco mixing block but the Taco doesn't heat water its self, it uses hot water heater. but they are $2000.00 plus. I like your idea for the other option with mini hot water heater. Could I just use my regular hot water heater? I could use a plate heat exchanger? I can get 2 for $100.00 on marketplace.
    Would a Hot water recirculating pump work? I has setpoint and thermostat. How ever it could contaminate water heater with "legionnaires disease" possibly.
  • Jmichael
    Here is a short blurb about Taco MIxing Block.
    The RMB-1 is a complete injection mixing system, combining a variable speed injection mixing control, injection circulator, system circulator and air elimination all in a single unit.
  • Kaos
    Kaos Member Posts: 847
    What is the hot water source? Some systems that use a desuperheater don't make all that much hot water, so you have to be careful with tapping it for heat.
    What temperature is the water heater kept at? You may not need the mixing device included in that pump block. Those are nice to mix down supply from a system running 180F
    Heat Link and others sell basic HX isolation modules.
    Adding a HX to your tank is not too hard either.
    Tee into the drain valve on the WH and into the hot out. A stainless pump with a check valve inside.
    On the radiant side, a pump, a pressure relief, and a means to fill and purge. You could adjust the WH pump rate to get a pretty accurate outlet temperature for the radiant.
    Or add a mix valve bottom example, if you want exact radiant temperature or the HW tank runs hot 140 or above
    If you use a plate HX on a water heater you need to leave a way to descale it occasionally.
    Jmichael
  • Jmichael
    I keep the water heater at 120. I am getting a new one soon so I am also deciding weather or not to get a heat pump. Although I don't know where all this money is coming from… I intend to do this all and move the water heater to a new location.
  • Jmichael
    Would something like this work if I could get one?
    https://ww
    w.xylem.com/de-at/brands/lowara/lowara-produkte/ecocirc/#close
    that looks like a Euro pump based on the union connections, if so it is probably a 230 V pump
    mattmia2 Member Posts: 15,519
    A second circulator and fittings for the hx add up fast. The second, small water heater if you fill it with a hose is probably the cheapest option.
    hot_rod
  • Kaos
    You can't use a heat pump water heater for space heat. The heat pumps on the those are very small (~4000BTU) and it would be running way more than intended. Even if it is enough heat, It won't last long like that.
    Jmichael
  • DCContrarian
    DCContrarian Member Posts: 1,361
    More crucially, a HPWH pulls heat from inside the building. Using it for space heating is like a perpetual motion machine.
    hot_rodJmichael