Hello folks,
When I built my house 20 years ago I was going to do underfloor heat. I piped 2nd floor with oxygen barrier pex. I also did my Primary bath encased in 2" mortar covered with granite. I then discovered Geothermal from a friend and changed to that because of the complexity of in-floor and ease of install of Geo. So here 20 years later I have a cold bath floor. Its still plumbed for radiant. Could I run the small single loop from my hot water heater with a mini type system or is it similar cost to do a small are verses large area? I came across the Taco radiant mixing block, which could be the answer if not for the price. I can live with floors as is, I just new there was a genius here to tell me what is possible.
Regards, Mike
Comments
-
A small electric water heater can work well for a small room. It may be less $$ than a HX block?
With the small 6 gallon tank, you can select the element wattage. They come with around a 1300- 1650W 120V, but you can downsize to slow down the cycling.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream4 -
Thanks for the answer, the cost of the mixing block is about $2000.00. It does everything with just 4 connections, that's why it looked interesting. What would be approx. cost of systems you show?
0 -
The mixing block doesn't do everything. You still need an air eliminator, expansion tank, purge valve(s), etc so if you have the space, I'd agree with Bob that a standalone water heater would be a better option financially than the mixing block. The tanks are only a few hundred dollars and can be purchased at any big box home improvement store
3 -
-
To be honest I didn't put expansion tanks on those small systems.
8 gallons of water going from 65°- 100°= .0048 X 8G= .0384 g of expanded water
Fill it to 5 psi, it may go up less than 10psi. With a 30lb relief you have plenty of room.
If you use just the T+P in the tank, at 150 psi you have a lot of safety room.
LWC is another piece that could be eliminated, the heater has a temperature safety. I used a lwc if the heater was above the piping.
A manual air vent on top of the tank is sufficient also.
It's fairly easy to find scratch and dent small heaters at plumbing wholesalers or big box stores. $150, or 1/2 of new price typically.
You need.
Tank
Pump
T&P gauge
Webstone dual purge valve
Setpoint control, use a digital like Ranco or Johnson Controls, Honeywell, etc.
Mics fittings
Depending on where you shop 500 bucks or less
Too bad you can't find these Laing units anymore. The heater, pump, temperature and safeties were all built in. You could literally connect the pex in and out of them.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Hot_rod
The Laing unit sounds like the Taco mixing block but the Taco doesn't heat water its self, it uses hot water heater. but they are $2000.00 plus. I like your idea for the other option with mini hot water heater. Could I just use my regular hot water heater? I could use a plate heat exchanger? I can get 2 for $100.00 on marketplace.
Would a Hot water recirculating pump work? I has setpoint and thermostat. How ever it could contaminate water heater with "legionnaires disease" possibly.
0 -
Here is a short blurb about Taco MIxing Block.
The RMB-1 is a complete injection mixing system, combining a variable speed injection mixing control, injection circulator, system circulator and air elimination all in a single unit.
0 -
What is the hot water source? Some systems that use a desuperheater don't make all that much hot water, so you have to be careful with tapping it for heat.
0 -
What temperature is the water heater kept at? You may not need the mixing device included in that pump block. Those are nice to mix down supply from a system running 180F
Heat Link and others sell basic HX isolation modules.
Adding a HX to your tank is not too hard either.
Tee into the drain valve on the WH and into the hot out. A stainless pump with a check valve inside.
On the radiant side, a pump, a pressure relief, and a means to fill and purge. You could adjust the WH pump rate to get a pretty accurate outlet temperature for the radiant.
Or add a mix valve bottom example, if you want exact radiant temperature or the HW tank runs hot 140 or above
If you use a plate HX on a water heater you need to leave a way to descale it occasionally.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I keep the water heater at 120. I am getting a new one soon so I am also deciding weather or not to get a heat pump. Although I don't know where all this money is coming from… I intend to do this all and move the water heater to a new location.
0 -
Would something like this work if I could get one?
https://ww
w.xylem.com/de-at/brands/lowara/lowara-produkte/ecocirc/#close
0 -
that looks like a Euro pump based on the union connections, if so it is probably a 230 V pump
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
-
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements