Correct false water line tank diameter

Dave52
Dave52 Member Posts: 24

I'm assuming if the tank diameter is at least as large as the connected EDR going to it, based on wet return pipe capacity's. Aware of the vertical requirements.

That should be a minimum.

Any other idea's?

Comments

  • mattmia2
    mattmia2 Member Posts: 11,237

    What? A false water line is usually just a pipe loop with an equalizer that keeps the return above the boiler's water line.

    What are you trying to do?

  • Dave52
    Dave52 Member Posts: 24

    This is all part of the previous post now moving forward further

    https://forum.heatinghelp.com/discussion/198723/old-church-combined-1-and-2-pipe-systems-needs-false-water-line#latest

  • Dave52
    Dave52 Member Posts: 24

    Have dim "A" all calculated out. Just getting a idea on diameter.

  • Jamie Hall
    Jamie Hall Member Posts: 25,358

    As noted, that depends on what you are trying to do with it. If it's just a false water line, it can all be the same pipe size as the wet return to which it is connected — including the required equalizer line. If it's to be a storage tank to augment the boiler storage capacity to compensate for slow or distant wet returns, that's another matter entirely, and the diameter is governed by how much water you need to staiblise the water line to within the needed range.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England