I believe the two vert pipes off of the LLH do go to the AH. That AH has its own circ if I'm not mistaken. Both the supply and the return lines from the AH will be hot do to convection of hot water in the LLH. Check the Pump ij the AH.
Ugh sorry, I just read through the comments and see this has been mentioned already.
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
0 -
Answeres and questions
- Do I need a circulating pump and is that something that is doable at this stage
- I have been in the house 1 year Feb 2024 system installed 7 years ago
- Tech said that the pump was clogged on Tuesday, again was blowing cold air came back 2 days later and said that it is now burnt out so he changed it
Attached more pictures
Thanks for the help
0 -
Have someone check the pump in the AH. Check if it's getting power during a call for heat. Then check if it's working. `If the pump is working the return will be significantly cooler than the supply. If you remove the cover of the AH you'll see the pump. If you remove the silver screw cap in the center of the pump you should see it spinning during a call for heat. You can spin it with a screw driver but if it's not spinning it's likely finished.
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
1 -
look at the last link I posted, your manual,
there is a circ inside the the top cover of the AH,
did you try to shut off everything else and force water to AH like I wrote above
known to beat dead horses0 -
I have not yet, will try tomorrow, I am also a little tentative as I don't want to mess anything up further but if you think this is a good idea and won't mess anything up I will try
0 -
uh, yeah, my force idea could bump air to somewhere working now,
known to beat dead horses0 -
There might be a bleeder in the air handler!
0 -
Do I need a circulating pump and is that something that is doable at this stage
It is now determined that you DO HAVE a circulating pump for the air handler and it is living within the air handler………..so you do not need one. What you do need to determine if whether this pump is working properly and, if so, to determine how to eliminate any air that may be in the loop between the boiler and the air handler.
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements