Air separator drawing air in? Circ pump causing low pressure leak?
In my shop I have hydronic floor heat. I originally installed the circulator pump after the air separator/expansion tank combo like everyone says to do but I've been getting air in the lines.
I've done countless overnight pressure tests on the system and have never found a leak. I suspected the air separator and tightened the air valve shut and ran it for a few days and when I opened the valve, very little air came out. After much testing, if I run the air separator closed and only open it occasionally to vent the system, it works fine. But if I leave it open while running it, like it's meant to be run, I end up getting more air in the lines.
I'm considering relocating the circ pump to the other side, before the boiler, in a "pumping to" scenario. I know that "pumping away" is the right way but I'm pretty frustrated. I don't want to keep running it with the separator closed because I'm not a fan of having to climb up to it to vent the system all the time and I didn't pay all that extra for that auto vent (twice - lol) just to have to do it manually - lol.
Is it possible that , with the circ pump being just beyond the air separator, it is causing a low pressure area that is causing air to be pulled in past the air valve on the separator? I've replaced the separator once and it didn't help. Any thoughts?
Comments
-
pictures
0 -
I presume the sequence of devices is expansion tant, air separator, pump inlet?
If that is the case, unless there is a significant restriction between the expansion tank and the air separator, the pressure at the air separator will be within a psi or so of the pressure in the expansion tank — provided that the expansion tank isn't bottomed out. You might want to check the expansion tank air pressure; it should be a pound or two below the static system pressure when the pump is not running.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
at some point if you have a good separator the system should be 100% air free. Is it non barrier Pex in the system? Any other auto vents?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Need pictures.
Sounds like your Expansion tank is not doing its job and where is the PRV attached to the system??
0 -
I'll get right on that. Thanks.
Yes. The expansion tank is mounted directly under the air separator and the circulator is directly after them.
The tank is at the factory 12# it came with. This is a closed loop system if that matters.
The system is apart at the moment but it has always run between 12 and 18#.Yes, the pex has the oxygen barrier and the system will run nearly air free if I keep the air separator bleeder closed. But it's designed to run with the bleeder open. And I'm designed to not have to climb up to bleed it off. 😄
"If some is good, then more is better and too much is just right!" ~ Shayf0 -
No PRV on this system. This is a closed loop system in my shop. Not connected to my house water service.
I didn't think to get photos of it. I plan to take some next time I'm out there."If some is good, then more is better and too much is just right!" ~ Shayf0 -
I doubt air is getting in. Or water would come out if the seal is broken?
If it is a Caleffi, or a brand made by Caleffi, you can get a check valve cap.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks for the replies guys.
I appreciate your time and attention on this matter.
Be well."If some is good, then more is better and too much is just right!" ~ Shayf0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements