Options for flexible radiator plumbing?
Hi Heating Pros,
I'm redoing my bathroom and in the past have had a hard time reconnecting the old iron pipe supply/returns to the radiator… As I re-do this bathroom, I would like to add some insulation in the old radiator alcove which means that the rad won't fall on the original positions… SO, I'm wondering what you would all do.
Obviously I plan on draining the system and them I'm wondering if I can keep some sort of rigid copper/metal piping from the radiator nipples DOWN through the floor, but once in the joist bay, I'm wondering if I can/should switch to PEX which will give me more flexibility and make the rad re-install easier when the time comes?
Is PEX A ok to use? or would I need the oxygen barrier kind? if oxygen, does it work/cut/crimp the same way as A which I'm familiar with?
What have/would you all do?
THANK YOU!
Jay
PS - existing iron pipe is 1" OUTSIDE diameter.. so 3/4" pex maybe?
Comments
-
Yes you would need to use oxygen barrier pex. Are those just standard cast iron tees in the picture? I see a patent date maybe like some older gravity system. I could be wrong
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company1 -
-
Me? I would figure out where the radiator was going to end up — I presume just a few inches, if that, further away from the wall? — and undo the existing pipe, cut the horizontals to the correct length, thread them up and put it all back together.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Those are probably "O.S." fittings, named for their inventor Oliver Slemmer.
Do not use PEX on this system. The fittings restrict the flow and the rad won't heat well. @Jamie Hall has the right idea.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Is that a plaster ceiling below?
If that is an outside wall, insulate the piping also.
Copper or pex may be easier for you to work with.
Figure out what those tees are, however. You want everything to work after you cover it up.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thank you all! Yes, a few things I forgot to include.. it's an old house (1911).. I took some better pictures of the fittings - looks like O/S on one side and "PATD FEB 1 98" (or maybe 95) on the other. 1898 :)
While the system (I think) has always been hot water (not steam), I do think it was gravity? based to begin with.. all the near boiler pipes in the basement slant a bit and are big fat cast iron.
Sounds like I SHOULD get my proper layout finalized, then re-do the correct horizontal lengths.. I was just looking to cheat a bit :) - and hopefully give a little more wiggle room through the eventual finished/tile floor.
0 -
Here are some resources:
Forum Moderator
0 -
-
Yep, I would have zero hesitation to take the iron pipe out back to a threaded fitting, as far as the closest O/S fitting (I wouldn't take that out). Then put in a threaded adapter and go from there with either copper or oxygen barrier PEX.
That iron pipe with the 1" outside diameter is 3/4" nominal size, 3/4" copper or PEX will have the same capacity.
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements