Severe condensation?

Bzak1pgh
Bzak1pgh Member Posts: 3

I have everything hooked up that I know of..but getting severe condensation in elbow at top. Am I missing something?

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,717
    edited January 10

    First of all, You posted in "Oil Heating". Is that space heater operating on Gas or Oil?

    If it is oil, then you have a single wall vent with no barometric draft control, that means that the due point in that flue with out diluting the combustion byproducts exhaust will be very low. You may have a flue temperature near the top of that stack at the roof line as low as 250°F. That will be a Condensation Generation plant on a major scale. You either need to add some additional air by way of a barometric draft control or you need to change to a double wall L vent so the vent pipe stays warmer (or both)

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • pecmsg
    pecmsg Member Posts: 5,512

    And get the heat exchanger on that antique checked.

    Bzak1pgh
  • Bzak1pgh
    Bzak1pgh Member Posts: 3

    I've got a barametric vent coming..had to order it. It's Fuel oil... not gas…shes an old one i had in my old house about 15 ywars ago...i just got it out of storage to help take the chill out my garage so i can work on my cars.… Seems that's what I'm missing. I've clean everything out in it and seems to be in outstanding shape!! Just wish the fan blew better than what it does, but a pedestal fan in front helps!! Thanks for all the help!!

    EdTheHeaterMan
  • HVACNUT
    HVACNUT Member Posts: 6,454

    Does that flue pipe say 30 gauge?

  • 109A_5
    109A_5 Member Posts: 1,909

    Gasoline vehicles in that garage ? Probably not a good idea.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    pecmsg
  • pecmsg
    pecmsg Member Posts: 5,512

    X-2 Thats the wrong equipment in the wrong place for the job!

  • PC7060
    PC7060 Member Posts: 1,521

    Be sure to maintain minimum flue clearance from combustibles. .