System 2000 sudden issue
We have a System 2000 Frontier ek1 system (oil) in our house that is about 6 years old. This problem just started yesterday (which was also one of the coldest days in the northeast)
All appears normal (at least to me) when looking at the unit, however it seems to be not heating the water sufficiently? Typically we can only turn the hot water in our shower to about 75% because otherwise it is , usually, too hot. We like that. Yesterday (and today) even with the hot water at 100%, it is just warm. Same with the sinks in the house. We have three heat zones… they have heat, but, again, not at full capacity. If I set the thermostat to 70… it will only get to 66 and stay there.
Greening
  • jringel
    jringel Posts: 52
    There could be a couple of reasons for this. In regard to the heating zones keeping up. Is the boiler continuously running? If it is then we may have to increase the firing rate to get you the BTU' needed to heat the home to 70. With you having issues with your heat and hot water this most likely the case. If the boiler is cycling on and off and the rooms still are not heating then the heating issue would be related to the distribution system. If this is the case our managers have a setting that can increase the water temperature by 20 degrees. If you could let us know what the boiler is doing as well as the temperatures showing on the boiler gauge and the manager we can help you reolve this issue.
    John Ringel Energy Kinetics
    szwedjGreening
  • I appreciate your response. The 70 was just an example, we typically dont go higher then 65-68…before yesterday though whatever the thermostat was set at 65, 66, 67, 68, etc…. the actual room temp would match it ..now the room temp on the thermostat seems to just get to 66 no matter how high I set it. The boiler is not continuously running, no. It's on and off… when it is on, it doesnt seem like it stays on all too long though. I am not sure what is normal… The temp gauge fluctuates from like 210 down to maybe 150? at different times. I
    Greening
  • jringel
    jringel Posts: 52
    It looks like you are not getting good flow through the bypass plate exchanger. This could be caused by a partially blocked plate exchanger on the boiler side or an issue with the circulator not moving enough water. If you have a digital thermometer you can use the diagnostic testing from the attached sheet to test the plate exchanger or you can have your service provider, call our tech support when they are at the house and we can walk them through it
    Greening
  • Robertw
    Robertw Posts: 93
    What type of heat emitters do you have? Are the returns hot when you say the room isn't reaching temperature?
    Robert W.
    Energy Kinetics
  • How are you able to tell that. Can I please have the number for Tech Support?
  • baseboard radiators…typical 80's house style ones…. I am not home at the moment but yesterday the returns did not feel hot.
    hilltown
  • jringel
    jringel Posts: 52
    That would be a good indication of an issue with the circulator. with the high supply temperature you have on the gauge the returns should be about 20 degrees cooler than the supply which would be between 160 and 180 degrees. I would recommend having a service company take a look at the system to verify it though
    rynoheatGreening
  • Thanks for your help.
    Greening
  • jhickey
    jhickey Posts: 9
    edited January 2025
    You were exactly right. I had a tech come and said the Taco 007e Circulator did not have the power light on when he first arrived… as he was taking the cover off to look at the connections, it came on and started pumping. Not sure why, does that mean it is probably bad? Everything seems to be running normally since, but he didnt really do anything (except put the cover back on) so naturally I am concerned if I am really out of the woods! I mean, it seems like it is…the tap water seems to be as hot as it was before this all started. Tomorrow mornings showers will be the real test. Three of us shower in the morning within 90 min..first shower was mostly normal… 2nd shower was starting to get lukewarm… 3rd person showering had less than lukewarm.. I need to keep an eye on the circulator pump light for a few days. Please confirm that the orange light on the 007e should be on when the green 'circulator' light is lit on the system manager? Am I right to assume that the green 'circulator' light (on the sys mgr) should be on whenever a zone output light (on the sys mgr) is also on? I guess I dont still understand how we had some heat and some hot water, just not full capacity, if that pump wasnt running?…(how would any hot water get from the basement to the upstairs without the pump?)… and he really couldnt explain it. He was just convinced that the circulator was the problem and it would be a good idea to replace it.…. He didnt have one as he is not really a sys 2000 tech, he has just worked on them from time to time…. He is going to get back to me with a price but in the meantime I just would like to understand if that is likely the issue based on the orig problem/symptoms I posted?
    Greening
  • jringel
    jringel Posts: 52
    whenever there is a thermostat or a hot water call to the manager the green circulator light should be on and the circulator should be running. the Taco 007e circulator that you have has an indicator light on it orange means its running, white means its air bound and red means that it is bound up. if you had a call on the manager and the circulator was not running or only running intermittently that could cause the problem you are having. you can replace the circulator with a new taco 007e or just a standard Taco 007 circulator. They are available at any local heating supply house.
    GreeningRobertw
  • Here is an update on my situation… everything worked fine yesterday. However, when I got up this morning I noticed that the room temps in our zones were again 2 degrees under the set temperature. When I looked at the system manager, the zones were calling for heat, the output lights were lit , the circulator light was lit, but the Taco 007e was dark. I tapped on the side of it a few times with my hand, it started blinking…then came on steady orange again. I did notice it blinked a few more times while I was standing there but then stayed on while the green light was on. Been running ok since (3+ hours). I know you are thinking, ' ok, its bad, I already said to replace it' and I get that. I was just wondering if this sounded typical of when they fail or could it be a loose connection and was wondering your thoughts on that? I have no issue getting the circulator replaced, I would just need to get someone to do it… I dont see any water shut off valves near it so I dont think it is prob something I would want to deal with myself… I like to try and handle these sort of things if I can, but I am always nervous about getting in over my head, if you know what I mean. Thanks.
  • jringel
    jringel Posts: 52
    That circulator has a molex connection that might be loose or the wires going into it may be loose. I would check to make sure the wires are making good connection first. if they are see if there is any play in the molex connection. if the wires and molex are tight then its a loose connection in the circulator and it will need to be replaced. if the molex feels loose taco does make a replacement molex connection that is black and will give you a better connection. At the end of the day you will probably need a new circulator but you can check this first.
    GreeningHVACNUTRobertw
  • Thank you!
  • Just closing the loop on this, my service company came out and replaced the circulator pump. All has been well for a week. Thanks again for the info provided here.
    RobertwHVACNUTjoncroteauRobert_H
  • mrcoder
    mrcoder Posts: 102
    An extra datapoint on the 007e: I just had mine replaced. The service company told me these circulators have a problem with the internal power connector, which tends to come loose. They are proactively replacing them all with a simpler circulator, with a simpler, more robust internal power connector.
    Over time, the return temp probe also often fails. It is an inexpensive part, literally takes 5 minutes to swap out,
    so it makes sense to at least check it, or swap it out while they are at it.
  • While the temperature sensors can fail, when they do the system will still operate in bypass mode so you will still get heat and hot water but lose the energy saving features that manager provides. Just as an FYI the old style sensors have been discontinued and have been replaced with a 10k Ohm thermistor which has become more of an industry standard.
  • mrcoder
    mrcoder Posts: 102
    From my experience, the return temperature probe failing did not put the system in bypass mode. It would just cause the burner not shutting down > 180F return, and cause an occasional E130 error. (A few times in a few months)
    BTW does anyone know where to source one of these, or what is the equivalent ?
    It is a silver bullet, ~ 5/8 " diameter, 2 2/8" long, with 3 wires (black, white and red)
    It has this written on it:
    2127
    05 - 0205
  • with the digital manager with the red dashes if the return sensor fails you should get an error 100 on the manager which puts it into bypass mode. The circulator will run constantly and the boiler will maintain the high limit temperature and there will be no delay in opening the zone valves. this will cause the boiler to run at a higher temperature but will allow the system to provide heat and hot water. With the display manager with the LCD screen if a return sensor fails you will get an error 100 on the screen and the system will go into bypass mode for 10 minutes to try to reaquire communition with the sensor after 10 minutes the manager will switch to an error 190 classic mode which allows the manager to operate on time instead of temperature like the original classic managers. Either way the failure of a return sensor wont allow the system to lockout or prevent heat or hot water to the house. The sensors are available direct from the factory and not at local part houses
    RobertwszwedjGreening
  • mrcoder
    mrcoder Posts: 102
    @Jringel, That is interesting… None of what you described above happened in my case. It is a fairly new ( <4 years) Resolute system, with the 70200 manager. Not the absolute latest firmware, I have a more recent spare manager, and I see that they changed some operational parameters to work better with Bio blends, and made the alarm contacts configurable between "on or off when a lockout occurs.
    What happened was what I described a couple of posts ago. I wonder if there are different failure modes for the return temp sensor? Some that the manager can detect, and others that it can't?
    For example abnormally low impedance? Just guessing, try to explain why my symptoms were different.
    I have never seen a sensor error message, except the occasional E130. I think the E130 caused the system to freeze up, and the power had to be cycled to get it going. As I recall, the burner did not lock out, ie did not require a reset. The burner ( Carlin x-pro ez) was in idle mode ( no call for heat) for a few hours until I noticed.