Issue with beckett oil furnace fan going on and off

Wayne1
Wayne1 Member Posts: 1

I changed air filter,cleaned sensor, burner seems to be fine and fan seems to run correctly while burner is on,it's afterwards it's on and off.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • yellowdog
    yellowdog Member Posts: 258

    What model of furnace? What controls the fan? When's the last time it was vacuumed out?

  • Grallert
    Grallert Member Posts: 952

    How often does the fan come on after the burner is off? How long does this on/off/on/off last? The burner will only go off for three reasons. The heat exchanger reaches a high limit, the thermostat is satisfied or the burner locks out on a safety issue. Can you show a picture? I'm curious as to what kind of fan limit controls are present.

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

  • HVACNUT
    HVACNUT Member Posts: 6,688

    If it's a fan/limit control, it's not uncommon for the fan to cycle a few times after the call for heat ends. The filter is clean, so the furnace is oversized, or incorrect ductwork, or dirty AC evaporator, or wrong blower speed.