New Mitsubishi system set up

rconkling
rconkling Member Posts: 57

Hello all and thanks in advance.

I just moved into a new construction condo with a pretty nice Mitsubishi HP city multi system and I want to make sure its settings are correct for best performance/efficiency.

The outdoor unit is the M Series - MXZ-4C36NA2-U1, with 1 PEAD A24AA7 or A15AA7 servicing the 3 rd floor bedrooms, and 2 M-Series - MLZ-KP09NA or MLZ-KP12NA-U1's servicing the main living area. Indoor unit sizing is unconfirmed because they list both as installed on the web portal.

Each indoor unit has a honeywell TH6320WF2003 thermostat with a PAC-US444CN-1 interface controller.

My understanding of the city multi MXZ is that is really a commercial VRF unit. Info on the system is quite limited online.

The thermostats are set up as a single stage gas system. Which just seems strange to me. But maybe thats where the interface controller comes in?

Is there a way to gain access to the system and see how the controllers are working or how they are setup?

My only other experience with a HP is a Daikin FIT, which I really like.

Im trying to find out what contractor installed the system and get info from them, but I also would like to verify what Im being told by them.

Cheers and Happy New Year!

Ryan

Comments

  • pecmsg
    pecmsg Member Posts: 5,545
    edited January 2

    mitisubishi has a contractor locator site.
    punching in the serial #’s may give the installing contractor information.

    Choose your service provider wisely.

  • Kaos
    Kaos Member Posts: 365

    Generally with modulating units, you want to use the factory communicating thermostat. These don't have the easiest user interface, so I can see why people would opt for a regular thermostat.

    You can get the regular thermostat working reasonably well but it does need to be configured properly.

    The themrostat should be set to 2 stage heat and cool (so lots of wires to the PAC) and the PAC configured properly. Without this, the units are simply on/off at full power which defeats the purpose of a modulating unit.

    For the PAC,

    you want to enable delayed off (30min is the best), fan to auto, stage1 operation to ramp (not full).

    Make sure the thermostat is also configured for two stage heat and cool.

    If they didn't run all the wires, there are wire expanders that allow you to have 7 wire control over regular 5 wires.

  • GW
    GW Member Posts: 4,896
    edited January 2

    Hi Ryan

    M Series - MXZ-4C36NA2-U1 is not a City Multi, it's an M series (residential)—-someone has their wires crossed somewhere. It's not a Hyper heat either, in which climate zone do you reside?

    PAC-US444CN-1thermostat interface—-that's a bummer, maybe the GC speced that and the installer had his hand tied. The MHK-2 is what you want. But what you have does the job

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • rconkling
    rconkling Member Posts: 57

    Sadly I wasnt given any options on the HVAC side of things and I have no idea who designed and spec'd the system. But I have no doubt that keeping costs low as possible were the priority.

    Based on what ive seen so far in the rest of the house, it will require some tinkering or replacing of parts to make it work as designed.

    I do know they plumbed a make-up air duct from outside directly to the PEAD, but I dont see any way to control it. The super mentioned no one uses it. I now see why.

    I live in Northern CA, Novato to be precise. Hyper heat is not required.

    Where would the PAC likely be installed?

    I do have 7 wires going to the thermostat.

  • Kaos
    Kaos Member Posts: 365

    It will be in or near the electrical panel of the indoor unit.

    You are in warm enough climate that fresh air without recovery is fine. Pretty much all new construction is tight enough that you do need mechanical ventilation. I would keep the fresh air feed open or if you have a CO2 monitor, adjust the opening to keep CO2 under 1000ppm. During wildfire season, you do want to closed.

  • rconkling
    rconkling Member Posts: 57

    Looks like the MHK-2 is a wireless thermostat. It appears to have a lot more functionality but I think Id prefer a wired connection since the wires are installed. Unless this can be modified to connect to the wires. But I dont see that in the install manual.

  • GW
    GW Member Posts: 4,896

    what you state is correct

    one rep once told me the Kumo adds more flexibility and functionality. They aren’t terribly expensive

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    rconkling
  • rconkling
    rconkling Member Posts: 57

    Thank you.

    I spoke with someone from the company that installed the system. They installed it to the plans they were given by the builder.

    He agreed that its not ideal and recommended a wired T-stat but said it would also need a interface module for it to operate.

    I may cave and use the MHK-2 since it comes with the interface module.

    Cheers

  • pecmsg
    pecmsg Member Posts: 5,545

    so the builder speced the equipment.
    that doesn’t work out well.

    rconkling
  • GW
    GW Member Posts: 4,896

    @pecmsg all new construction is spec’s by someone, isn’t it? Unless it’s a custom build but isn’t that getting rare these days?

    Everything has a pro and a con. Buying a condo- less decision making. Some people like it that way

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • GW
    GW Member Posts: 4,896

    interface module—-it doesn’t come with that.

    What you have now is called the interface module

    Well it does have a little dongle thingie, but most people wouldn’t call it an interface module.

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Kaos
    Kaos Member Posts: 365

    There are wired thermostat options as well:

    https://mylinkdrive.com/USA/M_Series/R410A_Systems-3/Outdoor_Equipment/R410A_Outdoor/PEAD_A24AA9?product&categoryName=R410A_Outdoor

    I remember those being a 3 wire connector but could be wrong, either way you have enough wires with the existing setup. The cost of a thermostat, never mind two, is high enough that it isn't really worth it. I would get the existing thermostat and PAC-444 set up the best you can and see how it runs first.

  • pecmsg
    pecmsg Member Posts: 5,545

    The GC doesn’t give a flying F#%k about the buyers energy usage or Comfort. ALL he cares about is HIS bottom line.


    really!

    rconkling
  • GW
    GW Member Posts: 4,896

    I’m unsure what you are asking, it’s not right or wrong, it’s just the way it is.

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • rconkling
    rconkling Member Posts: 57
    edited January 15

    I think I figured it out.

    On the PAC-US445 I have all the dip switches off. The installers had SW1-1 on which caused major short cycling.

    T-stat is set up for conventional electric 2 stage heat and cool, with T-stat fan control.

    Seems to be running lower fan speeds initially now which is nice.

    I may still end up with the MHK-2 in the near future.

  • Kaos
    Kaos Member Posts: 365

    There are screws that hold on the cover. You unscrew those to open and adjust the dip switches.

    rconkling
  • rconkling
    rconkling Member Posts: 57

    Thanks I finally figured that out. I thought they would be on the side, easily accessible.

    The system is definitely running differently. Ill see how it goes.

  • rconkling
    rconkling Member Posts: 57
    edited January 15

    Well so far its a complete failure to have SW1-1 turned off.

    Not sure what climate zone this is supposed to operate more efficiently, but it cant be mine. Although I guess efficiency and comfort dont always go hand in hand.

    The Ceiling cassettes never turn off, the fan runs off and on, but mostly stays on, even with no call for heat. So the room feels a lot colder due to the cold air movement.

    EDIT:

    I put SW1-1 back on and lowered the CPH from 9 to 6 during heating mode.

  • Kaos
    Kaos Member Posts: 365

    Multi splits have a nasty habit of not modulating the indoor unit properly, sometimes have to play with the settings and find one that gets you decent comfort.