Pumping AC unit down in winter
ChrisJ
ChrisJ Member Posts: 16,692
I need to pump a 5 ton cool only unit with a scroll down to move it. I'm sure the 20f ambient will make it easier on the condenser but I'm concerned about starting the unheated compressor.
Should I try to heat the compressor? Any tricks anyone could add?
I was thinking about letting a 1500w ceramic heater blow on the compressor for a few hours.
    pecmsg Member Posts: 6,041
    it should have a crankcase heater.
    just listen or Throttle the suction service valve valve maintaining 25-50 #’s
    ChrisJ
    EBEBRATT-Ed Member Posts: 17,730
    Not supposed to pump down a scroll. You can pump it down partially and then recover the rest.
    When you evacuate the lines set and open the valves then warm the compressor if it is cold out. Depending on the temperature. You can also throttle the suction valve as @pecmsg said.
    When they first came out with scrolls they said they could "eat liquid" and no CCH was needed. After compressors were failing CCHs became the thing. Carrier especially was famous for units with no CCHs.
    ChrisJ
    you can use Emerson’s method……..
    3 quick short starts
    ChrisJ
  • ChrisJ
    I had thought about disconnecting the start cap and letting it go out on overload a few times but I'm betting it won't make enough heat to matter.
    How short are the starts, like 5 seconds each?
    After doing the 3 do you wait for the oil to settle down or just let it run?
  • ChrisJ
    Off the top of my head I think Copeland said it's fine as long as you don't go below 50 psi. I was going to aim for that and then recover the rest.
    I'm betting as long as you keep the low side slightly positive the scroll would be fine.
    there 1 or 2 second bursts 3 times then run.
    ChrisJ
    scrolls have very little oil in them and it doesn’t take much to heat it.
    ChrisJ
    HVACNUT Member Posts: 6,754
    If you're using the recovery machine anyway, why not just recover all of it? Is the condenser moving to a new location where a change in pipe length will effect the existing charge?
    mikeapolis
    Easier to just pump all the refrigerant into the condenser with the compressor.
    ChrisJ
    Unless the condenser won't hold the charge
  • mikeapolis
    mikeapolis Member Posts: 48
    R22 or 410?
  • ChrisJ