I have a York furnace, model GY9S100C16UP11J that has stopped working.
4 flashes on the controller board-limit switch open
Jumped limit switch, no joy.
Jumped pressure switch, still no joy.
Bad controller board?
The furnace will run for several hours if turned off for 6 or 7 hours…
Anyone have any ideas?
Comments
-
Do you have a picture of the wiring diagram? There may be more than one limit switch.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Sorry, I don't have a wiring diagram.
0 -
I'm not sure if this is your system diagram, but it is for a York furnace and it appears that there are 4 switches on the "limit" circuit that can be "open". ILPS is the burner box pressure switch, LS1 is the primary limit switch, LS2 is a limit switch on the inducer fan and ROS1 is a roll out switch. If you check continuity of each switch and check if there is a reset button on each of them, you may find your problem.
That circuit starts at Pin # 1 on the 12 pin Molex plug as a Red Wire and goes to the LS1and then to LS2 where it splits to 2 white wires. One of the white wires goes returns to pin 7 on the Molex and the other white wire continues to ILP where it connects to a blue wire that returns to Pin 10 on the Molex. Check those 4 limit switches to find your problem.
EDIT: ROS1 is connected with a brown wire to pin 11 on the Molex and a black wire to pin 2 on the Molex. that may also have a reset button in the center of it.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Thanks! On it…
0 -
ROS1
is connected with a brown wire to pin11
on the Molex and a black wire to pin2
on the Molex. that may also have a reset button in the center of it.This is what a limit with a manual limit
might look like
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
-
Can't be a manual reset limit as the op stated if it is shut down for 6-7 hours it will then run.
0 -
Hello gurn1050,
" The furnace will run for several hours if turned off for 6 or 7 hours… "
With these symptoms is could be a bad (failing) solder joint on the control board.
Not sure if this is applicable to your unit. You did not mention the LED color.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Update and a question…
I had a HVAC dude come out and determine it was the control board, happily paid diagnostic fee…
Placed a 1/2 down payment for the board and installation as the unit is in a vacation home fairly far from my primary residence, but a few days later was told it would be a week before the part would arrive.
In the mean time, temperatures dropped, and my remote sensors detected temps very close to freezing, so I ordered some parts overnight, and replaced the board (and for good measure, both limit switches and the flame rollout switch)
Unit now works, and no pipes were frozen.
Thanks for all the advice (i also checked the condensate drain and it was fine)
Now, what to tell the HVAC company?
0 -
Well on a good day, if they ordered the board and they don't want it, maybe restocking charge. A not so good day you now have a spare board. I would call them ASAP, especially if there is a scheduled appointment to cancel.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 425 Carbon Monoxide Awareness
- 108 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 960 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements