Riello F3 burner bad from factory??
has anyone else experienced bad burners on brand new installs lately? Got a weird one where the burner is kicking on and off til it finally will just stay running. Only been in service for a month. It hard starts as well. Spoke to my local supplier about it who has a very knowledgeable guy working there who said they’ve been experiencing this and they’ve tried everything to resolve it but so far nothing they come up with can fix it. They have to replace the burner entirely. Any info would be great!
How is the heater vented? Thru a chimney or is it using a power vent?
Never had a bad burner. Have had bad parts but I can remember the last time I've had anything faulty on a new burner. Very likely a set up issue.
Never had a bad burner. What's "bad"on it? The burner motor? Oil pump? Control? These are all easily replaceable parts that don't require an entire burner replacement.
I agree that the problem is likely something related to the installation. They are not plug and play. Everything needs to be checked during commissioning and adjusted for that particular installation. Pump pressure and vacuum on the suction line need to be verified. Combustion needs to be checked. Draft checked and adjusted. Static pressure and temperature rise need to be checked and airflow adjusted on furnaces. It's a process.
One time I had a defective Beckett Genisys primary control on a new boiler. But that's one instance in 20 years.
2 -
are you a burner dude? 20 something years ago I got my clock cleaned on a Beckett NX balanced flue . The vendor let me have a Riello.
Riello’s don’t like too much draft, too much air, too little oil pressure. A bum nozzle will ruin your day0 -
Lean fire ?