007 Circulator “getting tired”?
grocha88
grocha88 Member Posts: 3
I came across a one zone hot water gas boiler in a relatively small house (one floor, five rooms, base board) the house was heating very slowly, no air in system. I noticed the circulator was extremely hot to the touch similar to a siezed motor or air locked system. My question is: are circulators able to “begin failing” and not just completely fail?
  • PC7060
    PC7060 Member Posts: 1,804
    yes, any motor with bearings can degrade/fail over time causing pump to drag; increased friction will also overheat pump.
    grocha88
    hot_rod Member Posts: 27,445
    More apt to be a seized circ and maybe gravity flow doing the heating. Or air locked.
    When they seize, or air lock you basically have a 78W heater.
    Being a wet rotor, fluid cooled design they run pretty close to the system fluid temperature, if fluid is moving through them.
    An simple amp draw check would tell you more.
    grocha88SuperTech
  • Dave H_2
    Dave H_2 Member Posts: 622
    You could also take a look at the age of the circ, there should be a date code stamped on the electrical box showing a month and year of manufacturing.
    Dave Holdorf
    Taco, Inc
    grocha88
  • Lance
    Lance Member Posts: 334
    as always there can be other reasons. I have found too many new small pumps on systems that had B&G 100 on them. And flow checks. I started checking pump curves against the system head calculations and find some barely meeting the requirements. So bad or wrong pump, or other should also be considered.
    grocha88
  • grocha88
    @hot_rod thank you, I took that amp draw and found 1.5 amps while rated at .75!
  • rick in Alaska
    rick in Alaska Member Posts: 1,524
    How is the water pressure? If the pressure is down to zero, it can cause issues.
    Rick
    grocha88