007 Circulator “getting tired”?

I came across a one zone hot water gas boiler in a relatively small house (one floor, five rooms, base board) the house was heating very slowly, no air in system. I noticed the circulator was extremely hot to the touch similar to a siezed motor or air locked system. My question is: are circulators able to “begin failing” and not just completely fail?
Comments
-
-
More apt to be a seized circ and maybe gravity flow doing the heating. Or air locked.
When they seize, or air lock you basically have a 78W heater.
Being a wet rotor, fluid cooled design they run pretty close to the system fluid temperature, if fluid is moving through them.
An simple amp draw check would tell you more.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
-
as always there can be other reasons. I have found too many new small pumps on systems that had B&G 100 on them. And flow checks. I started checking pump curves against the system head calculations and find some barely meeting the requirements. So bad or wrong pump, or other should also be considered.
1 -