Hi everyone do I need recirculating pump on heating return line to drop pressure

I have 9 Radiators same time the pressure go up to 36 PSI

I Have 1 Taco 007-F5 On supply line

Thanks

Comments

  • GGross
    GGross Posts: 2,119

    You need an expansion tank. Can you show a pic of the piping as installed?

    SuperTech
  • Thank you this it’s my setup

  • marcelt66
    marcelt66 Posts: 12
    edited December 2024

    Hi I notice when the boilers runs for heat if I open hot water faucet pressure go up to 36 PSI and safety valve it,s opening making noise

    Thank you

  • neilc
    neilc Posts: 3,214

    what year is the Navien? maybe heat exchanger is leaking thru(?)

    known to beat dead horses
    SuperTech
  • 2023

  • pedmec
    pedmec Posts: 1,491

    Your missing a PRV and Backflow

    GGross
  • GGross
    GGross Posts: 2,119

    Is that expansion tank piped to both the heating system and the DHW side but just valved off? what is the pressure on that expansion tank? it should say on the label somewhere the precharge, if someone changed it they would write it in sharpie or something. You also have a bunch of valves partially closed off for some reason?

  • Expansion tank it’s like 15 Psi from 40 PS

    From tank it’s pipe to heating not to DHW

    Those partials closed valve I did to reduce pressure in

    Do I need to connect expansion tank to hot water supply to

    Thanks

  • Thank you for all your help and suggestion this it’s what I did

    Install Backflow and PRV

    I Hope this will bring down the pressure

  • I did take out check valve and still the pressure go up to 36 PSI

    I have to get Gordon Smith it’s licensed to contact NAVIEN

    Thanks everyone

  • Hi everyone this it’s what I did so far so good

    Install a PRV on Auto Feeder Inlet (Make-up-Water) and so far issue that I use to have it’s gone

    Thank you everyone have a healthy and prosper new year